Benn,

I have a little experience from about a decade ago. Don't know how useful it 
will be though.

AEE and DC Power used to team up to supply power for a three-day outdoor music 
festival in Mendocino Co, CA in the mid 90's and early 2000's. Music from 5-8PM 
on Friday, and from 11AM-10PM on Sat and Sun.  I don't know how big the crowd 
was  - 5-6000 I would guess.

We would bring a rack-mounted 12kW Exeltech MX inverter set-up (24V and not 
even N+1 redundant) and 5-6kW of PV (a lot of 120W modules). DC Power would 
bring two big tractor-trailer loads of industrial wet-cell batteries (I have no 
idea what the total amp-hours were, but a hell of a lot).

The sound crew would show up each year with a bigger set-up, even though we 
warned them that the power supply was limited. Stage lighting was left on 
generators running biodiesel.

The last year that we did it, the sound guys showed up with a sound system 
rated at 14kW. It drew 6kW just being on with no sound. Not even a hint of buzz 
or hum from the inverter power. The MX is good stuff.

I nervously watched that Exeltech all weekend as the bar graphs on each power 
module stayed in the red over-load range for most of each band's set. When the 
drummers or bass players would go nuts it was all red lights. We were measuring 
up to 600A of current flowing through the four pairs of 4/0 cables coming from 
the batteries, and a good bit of voltage drop as the cables were at least 30' 
long. The inverter was seeing less than 24VDC most of the time. The cooling 
fans on the MX modules would run for 20-30 seconds, and shut off for a minute 
or two and then come on again. This is with temps in the upper 90's, and the 
inverter sitting on the ground under the stage. Even with all this torture, the 
Exeltech never even hiccupped, which was quite impressive. The sound engineer 
was hollering at us that the inverter was clipping off the high notes, but 
neither I, nor the audience ever noticed. All I could do was shrug and tell him 
that he was warned about limited power availability. The music was great.

By the end of the weekend, those batteries were pretty drained, so it's hard to 
actually say that the show was "solar powered". Sitting around with a few beers 
afterwards, we all agreed that the ranch owners could install a 2kW grid-tie 
system on a tracker at the concert site and that system would produce all the 
energy needed for the show in a year's time, likely including the energy use 
for the lighting and by the vendors. This would have required that utility 
power be brought to the site, which would have been a rather expensive deal, 
but would have made more sense, and would have made it a more truly 
solar-powered event.

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Wednesday, April 27, 2011 3:51 PM
To: Wrenches
Subject: [RE-wrenches] PV powered music festival

Wrenches,
I have been asked about sizing PV systems for a couple different music 
festivals that have been run solely off of generators in the past.  The problem 
i'm having is determining the energy consumption of music/stage (amps, 
speakers, lights, etc...?) loads as well as concession.  The organizers have 
never considered the kwh of electricity used and it has never been metered.  I 
believe the attendance of one festival is expected to be in the range of 5000 
and the other closer to 15000 over the course of a weekend.

Do any of you have any experiences in this area?  How were the loads determined?

No doubt that generator back-up will still be needed, to what extent, will be 
determined.  So what we're looking at would be a temporary off-grid PV system 
with generator back-up...

Any suggestions on how to proceed with this one?

benn

DayStar Renewable Energy Inc.
b...@daystarsolar.ca
780-906-7807
HAVE A SUNNY DAY


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to