My general rule of thumb on batteries is that 100 cycles @ 80%DOD equals about 
1 year in an avg. off grid system.
Most of the AGMs I see are rated at about 300 cycles, the L16s maybe 550 to 600 
cycles, Trojan T105 is 750 cycles, and the HUP is rated at 2100 cycles at 80% 
DOD.
My experience over the past 20 years seems to hold to this rule, although I've 
had the L16s only go 4 yrs., and the T105 die at 5 yrs.
I've definitely had AGMs last longer than 3 yrs, especially in GT systems 
though. 
I would think the batteries' avg temp over the 24 hr period would be lower than 
100F down in the ground, but I don't live there.
Have you considered a passive cooling system like the Cool Cell from Zomeworks?
I would think if you're going to put serious money and electrical energy 
towards cooling, I might look at a water cooled setup:
PEX tubing coiled between the batteries, small DC pump to a radiator and fan.
Be more direct and efficient than an AC unit.

Just tossing out BS ideas at this point.......

R. Walters
r...@solarray.com
Solar Engineer




On Apr 21, 2011, at 3:19 PM, Starlight Solar, Larry Crutcher wrote:

> Hi Ray,
>  
> Absolutely: Battery charging 101 = temperature compensated charging, no 
> exceptions.
>  
> I too thought of underground storage but the temperature is still above 100 
> degrees at 6 feet down. It is really hot in the Baja!
>  
> I disagree about AGM life. I have heard others say this about AGM's but it 
> has not been our experience. I personally have a 900AH bank that is 6 years 
> old and shows little signs of aging. I have equalized the batteries twice to 
> keep the capacity up(each one individually, constant current, unregulated 
> voltage) We only sell and install battery based systems at our retail store 
> and about 50% of sales are AGM batteries. We have found that they have 
> similar life to flooded batteries but with great benefits.
>  
> Yes, some L16's just don't hold up well but I am talking about entire banks 
> failing all at about the same age.
>  
> Thanks for your reply.
>  
> Larry
> ----- Original Message -----
> From: R Ray Walters
> To: RE-wrenches
> Sent: Thursday, April 21, 2011 1:50 PM
> Subject: Re: [RE-wrenches] Air conditioning for batteies in high 
> temperatureclimate
> 
> Are you using temperature compensation? It lowers the voltage when its hot.
> Also, have you considered setting the batteries in a below ground vault? I've 
> had good luck with in floor battery boxes.
> Finally, AGMs and L16s just don't last very long anyway. AGMs maybe 3 years, 
> and L16s I've seen die in under 5 years and we get to 15 below zero.
> My suggestion: temp comp, ground vault, HUP or equivalent cycle life.
> 
> R. Walters
> r...@solarray.com
> Solar Engineer
> 
> 
> 
> 
> On Apr 21, 2011, at 1:22 PM, Starlight Solar, Larry Crutcher wrote:
> 
>> Hello Battery Wrenches,
>>  
>> Over the years I have had several battery banks in Baja and Sonora Mexico 
>> fail in just 36 to 48 months. These have been L16 or 8D AGM or flooded 
>> banks, 24 and 48 volt systems. The charging systems are working properly and 
>> programmed to manufacturer recommended set points and discharges are rarely 
>> over 30% DoD.  Some batteries are only used on weekends, some are discharged 
>> daily.  I believe what is affecting the short life is the high temperature 
>> they live in for 5 months each year. Temps. can hit 115 F in vented battery 
>> rooms. I have been thinking about a small air conditioner and insulated 
>> battery box to keep the battery at no more than 80 F. There are some 
>> portable units that draw about 600 watts and the run time would be very 
>> little with a highly insulated enclosure. There is ample power to do this on 
>> the home I am changing batteries in now. Has anyone done this and gained 
>> longer battery life?
>>  
>> Best Regards,
>> Larry Crutcher
>> Starlight Solar Power Systems
>> 
>> powered by STARLIGHTâ„¢
>> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org