Kristopher,
This is not that uncommon on gensets that are close to max output during the 
bulk charge runup to absorption. If the regulation let's the frequency pull 
down the clock will slow down also. If the no load frequency is set higher than 
60HZ so the motor pulls down to this RPM under heavy load the motor may run 
well above 60HZ as the amps taper off and the clocks run fast instead of slow. 
There may be adjustment on the fuel setting on the genset but he probably has 
his choice of too fast or too slow depending on which charging phase he wants 
at dead on 60HZ.
Nathan Jones
Power Source Solar Inc
Springfield, Mo

On Mon Apr 4th, 2011 4:51 PM CDT Kristopher Schmid wrote:

>I have an off-grid client who tells me that his clocks lose about 1 minute
>per hour while he is running his backup generator.  Has anyone seen this
>before?  Do clocks use the zero crossing on a 60Hz wave for keeping time and
>could a frequency discrepency in the generator cause this?
>
>My thanks to the brain trust...
>
>Kris 
>
>Legacy Solar, LLC
>864 Clam Falls Trail
>Frederic, WI 54837
>715-653-4295
>sol...@legacysolar.com
>www.legacysolar.com 
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to