Jamie,

 

The 6kVA imbalance limit, as you point out, is for 120V/240 split phase 
services, not 3-phase. It comes from California’s Rule 21 interconnection rules 
adopted by each California utility. As the technical facilitator of the 
development of Rule 21, I had a lot to do with the 6kVA number. It was based on 
the largest 120-Volt inverter that could be placed on the smallest available 
service. It JUST happened to coincide with the size of my Trace Engineering 
SW5500 inverter—funny how that works out.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jamie Johnson
Sent: Friday, December 10, 2010 12:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] feed-in imbalance

 

Marco,

 

I believe some of the discussions in the past had to do with the old 6kW 
imbalance limit that is used by several utilities on a 120/240 small 
residential single phase transformer. (don't remember the CA utility that came 
up with this)

I had this discussion with our local utility (FPL) recently and they look at it 
on a case by case basis due to the many variables involved with 3 phase power 
distribution, such as the size and type of transformer(s), 3 phase loads on the 
premises, the harmonic distortion if any on a shared 3 phase transformer, core 
saturation, load balancing, etc.

 

If you install a system in the FPL service area that is not balanced and either 
the harmonics or voltage is out of spec as a result (yes, they do test them), 
then you basically have 2 choices, balance the system or pay to upgrade the 
service drop and transformer.

 

There has been talk of testing various 3 phase transformer(s) to determine the 
maximum/safe out of balance configuration by our local utility, however, again 
there are a lot of variables, so it would be difficult to cover every scenario. 
 And this usually is only an issue on small 3 phase transformer(s).

 

I think that the 8,9,10TL 208v inverter has a load limiting ability that is 
incorporated in the inverter when you install 2 or more inverters, and it is 
programmable to limit the output of a single inverter to 6kW.  I believe you 
have to purchase the additional communication cables from SMA (cables available 
after the first of the year? or so I have been told).  Also, the design 
parameters seem a bit limited on the TL's.

 

Jamie

 



 

 

-------- Original Message --------
Subject: [RE-wrenches] feed-in imbalance
From: "Marco Mangelsdorf" < <mailto:ma...@pvthawaii.com> ma...@pvthawaii.com>
Date: Fri, December 10, 2010 2:00 pm
To: "'RE-wrenches'" < <mailto:re-wrenches@lists.re-wrenches.org> 
re-wrenches@lists.re-wrenches.org>

Now that SMA has come up with their new 8, 9 and 10 kW transformerless line of 
single-phase 120/208V inverters, it brings up the question once again about how 
practical and wise it is to have one or two of these inverters feed into a 
three-phase service.  That is, is such an unbalanced feed much, if any, of a 
big deal?

 

I spoke to my consulting E.E. about this and he said that the large majority of 
utility-provided transformers are so large these days that an unbalanced feed 
of, say, a 10 kW inverter that only has output power through L1 and L2 should 
not present a problem.

 

Any other thoughts out there on this matter?

 

Thanks,

marco 

 


  _____  


_______________________________________________
List sponsored by Home Power magazine

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org

Options & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out participant bios:
 <http://www.members.re-wrenches.org> www.members.re-wrenches.org

<<image001.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to