C40 charge controllers used to have that problem too; if battery voltage 
dropped so low that it didn't think it had a battery to charge, the whole 
system just sits there crashed, batteries sulfating, sun shining....(customer 
stewing....)
I'd just charge them on a 12 v automotive charger, 2 at a time. You can attach 
the leads to any 12 volts of series connected batteries, without having to 
disconnect all the cables. I would remove the main pos cable though. 
I've even jumped my truck to the battery bank before with jumper cables, just 
be careful and check your charge rate with an amp meter. Heat and gas from a 
dead cell in a sealed battery can blow the top right off the battery! You might 
just need 30 minutes per 12 v set. (2 Hrs total?)
When you get each battery up close to 6 v, you can probably get the system back 
up on the Sunny boy, unless any of the batteries have dead cells (won't charge 
over 4 or 5 volts per 6 v battery)
If that's the case, you should consider replacing the whole set. My 
understanding is that AGMs don't like to sit for long periods of time 
completely discharged. If they're not toast already, they definitely have just 
had their life severely shortened.

R. Walters
r...@solarray.com
Solar Engineer




On Nov 17, 2010, at 7:54 PM, August Goers wrote:

> Hi All Battery Friendly Wrenches -
> 
> We have a situation I haven't crossed yet - we have a Sunny Island grid tied 
> battery back system system with a 48 V battery bank consisting of eight 6 
> Volt AGM batteries. The charging breaker feeding the Sunny Island in the main 
> electrical panel was shut off by another contractor for about 3 months which 
> caused the Sunny Island to slowly drain the batteries until it fully shutoff 
> in order to protect the batteries. The bank now reads 24  Volts. That's low! 
> The Sunny Island is, according to SMA, powered directly from the battery bank 
> and won't even turn on. SMA tech support is recommending that we charge the 
> batteries and then turn the system back on. 
> 
> Any ideas about the best way to charge a 48 V battery bank?
> 
> Thanks for your advice,
> 
> -August
> 
> -- 
> August Goers
> VP, Engineering
> 
> Luminalt Energy Corporation
> 1320 Potrero Avenue
> San Francisco, CA 94110
> O: 415.641.4000
> M: 415.559.1525
> aug...@luminalt.com
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to