Hello Wrenches,

Looking through the archives on using a Megger for testing modules, it appears that it is best to keep voltages to 500VDC. I read all that I could find.

Talking to a Sanyo representative, I was told that keeping test voltage under 600 would not void the warranty or be an issue with UL. He said they have tested Sanyo modules up to 1000 VDC with no problems.

As a final test on a system, I want to Megger test the array from the terminations at the inverter. The approach I'd plan to use is:
   * Clamp the Fluke 1587 negative to the enclosuer ground.
* Put the positive test lead to the negative conductor from the array and test * Put the positive test lead to the positive conductor from the array and test All tests would be done at 500 V. The modules are illuminated, but there is no significant reading from either positive or negative terminal to ground. * The conductors would be removed from their terminals at the inverter and be in free air. * The conductors would be continuous through the string of 10 Sanyo 210 modules.
My questions are:
   * Does anyone see a problem in this approach?
* Since the array often has 500 VDC open circuit readings and shows no indication of a fault whatever, would this test accomplish anything more than the standard voltage to ground tests I've already done?
   * Is there any danger to diodes or other PV components?
Thanks in advance.

Drake   
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to