Greg,
I've already done as you've suggested. We are on record for opposing the choice. The Navy (well, the civilian Navy employee who wrote the RFP and controls the contract) is firm on doing VAWT's.

The GC is being generous with offering to buy the turbines and carry the VAWT warranty. Looks like I'll take them up on it.

Thanks for the feedback
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
ke...@whidbeysunwind.com
360-678-7131


On Oct 21, 2010, at 7:13 AM, g...@remotepowerinc.com wrote:

Kelly,

I've never seen one or heard of one that produces power or lasts. If you install these your name is on them. If they don't work it reflects on you and your business. I'd write the prime contractor a short note letting them know that you cannot find a VAWT that you can recommend with a clear conscious and because you don't want he and his company to wind up with a
black eye, your not going to recommend a VAWT to him for purchase.

If he's smart he'll tell the Navy he can't get a knowledgeable person with
a conscious to sell him one and they'll do the right thing and either
install a HAWT of good lineage or more solar.

Best,

Greg Egan
Remote Power Inc.

Message: 1
Date: Wed, 20 Oct 2010 15:16:46 -0600
From: Dan Fink <dan...@hughes.net>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] VAWT recommendation
Message-ID: <4cbf5c3...@hughes.net>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed

Kelly;

I would insist on a years worth of actual wind speed versus energy
output data performed by an unaffiliated third party, before even
touching this project with a 10-foot gin pole.

DAN FINK
Buckville Energy Consulting LLC

Kelly Keilwitz, Whidbey Sun & Wind wrote:
Wind wrenches,
We have a subcontract to install 30kW of VAWT, along with 30kW of PV for
the Navy. The Navy specified Helix Wind turbines, and is adamant on
sticking with VAWTs, although they may accept an alternative. The GC we are working under is sufficiently scared of Helix to look for a viable
alternative. Are there any?!

The GC has done some research and wants to use the UGE-4K from Urban
Green Energy http://www.urbangreenenergy.com
It's an H-style lift machine that appears to have several European
certifications on safety, power performance, noise, and vibration.

Anyone know anything about these turbines or company? UGE's address is
NY. Roy?

Thanks,
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
ke...@whidbeysunwind.com
360-678-7131
begin_of_the_skype_highlighting 360-678-7131 end_of_the_skype_highlighting



------------------------------

Message: 2
Date: Wed, 20 Oct 2010 16:17:36 -0600
From: benn kilburn <b...@daystarsolar.ca>
To: Wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Mounting Enphase when using S-5-PV Clamps
Message-ID: <col121-w2359be547c2d1a3c956ce5ad...@phx.gbl>
Content-Type: text/plain; charset="windows-1252"


Not a lot of you guys in the field today 'eh? I was just checking a spec on my laptop and noticed i had a wireless signal and a mailbox full of
great feedback, thanks again everyone!!!
I'll go over all the details from everyone a little more when i'm done on site for the day. For a few of you i just wanted to show you this link to the S-5-PV clamp, which is different from just the S-5! clamp > Click here to learn more. < The S-5-PV does not need rails, the mod frames sit on the 'mounting disc' which can accommodate one or two modules. BUT,
with the Enphase system, this leave no where to mount the inverters.
Bill made a good point; save this mounting method for string inverter
systems.  We are now planning this project using just the S-5
clamp/L-foot/rail system.  No problems.
Back at 'er!
benn
DayStar Renewable Energy Inc. b...@daystarsolar.ca780-906-7807 HAVE A
SUNNY DAY







Date: Wed, 20 Oct 2010 12:34:56 -0600
From: al...@positiveenergysolar.com
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Mounting Enphase when using S-5-PV Clamps









   We have used these for years. They work better than wire ties, but
the rubber liner deteriorates over time, so install them as if there
   is no rubber protection on the loom clamp.






       Allan Sindelar

           al...@positiveenergysolar.com

           NABCEP Certified Photovoltaic Installer

           EE98J Journeyman Electrician

           Positive Energy, Inc.

           3201 Calle Marie

           Santa Fe, New Mexico 87507

           505 424-1112

           www.positiveenergysolar.com




   On 10/20/2010 11:53 AM, jay peltz wrote:

     If this helps,



I just installed a system and used 3 different size loop clamps (
     del city) which worked really well.



     I used 3/8" for single wires, 3/4 for 2 wires and 1" for 3
and also for the connector, worked really well, made it all very
       clean.
     I attached them with SS tek screws into the rails.



     jay



     peltz power



         On Oct 20, 2010, at 9:40 AM, Mark Dickson wrote:




                 Just
                       finished one. . .  Direct Power recommended
                       drilling and bolting directly to the aluminum
                       rails--easy and solid.  Although, I was not
                       happy about all the wire management that went
into it though. Sure would be nice if somebody
                       came along and made some integrated wire
                       raceways!!!
                 It was
amazing how many blank stares I got from racking manus at SPI, when I asked them if they had any in the works. Most just kept pointing to their
                       wire clips and pretended not to know about the
                       NEC requirements.


                   Best regards,

                   Mark Dickson,
                   NABCEP Certified Solar PV
                         Installer ?
                   Oasis Montana Inc.















_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/b21a25fc/attachment-0001.htm >

------------------------------

Message: 3
Date: Wed, 20 Oct 2010 15:39:36 -0700
From: "Hans Frederickson" <h...@fredelectric.com>
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <e8cda5f561974bd493d879c6c8db8...@frederickson.local>
Content-Type: text/plain; charset="us-ascii"

Kris has a good idea. Installing 2x backer blocks on the I-joists will not only give you more depth for your lag screws, but it will strengthen the
roof framing as well. Also, as Kris recommends, check with the
manufacturer
for nailing patterns, etc. I was dealing with some BCI joists this past summer and I was pleased that Boise Cascade has structural engineers on
staff that are eager to help, and can email you approved drawings for
reinforcing the joists.

-Hans

 _____

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kristopher
Schmid
Sent: Wednesday, October 20, 2010 1:33 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] The perfect solar ready roof


What about screwing in double 2x6s flush to the roof deck between the
beams
where your feet will attach and lag bolting into that? Definitely check
with the beam manufacturer first, though.

Kris

Legacy Solar
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
sol...@legacysolar.com
www.legacysolar.com

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Scott
McCalmont
Sent: Wednesday, October 20, 2010 12:00 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] The perfect solar ready roof


In general, you shouldn't drill or cut the flanges on engineered wood
beams.
I think that eliminates lag screws into the rafters. They probably
wouldn't
have the same pull-out strength as a lag screw into a conventional rafter,
either.

Scott


On Oct 19, 2010, at 7:58 PM, Chris Daum wrote:



Dear Wrenches:

I have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those (sort of) particle board I-beams covered with 1/2" plywood (and shingles). What's the best metal roofing you could suggest--and would you beef up the
wood to lag into?

Thanks for all your input.


Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>




-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/9e73e457/attachment-0001.htm >

------------------------------

Message: 4
Date: Wed, 20 Oct 2010 16:17:51 -0700
From: "Kelly Keilwitz, Whidbey Sun & Wind" <ke...@whidbeysunwind.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] VAWT recommendation
Message-ID: <982a09ba-d184-4000-8eb3-ea570ef5b...@whidbeysunwind.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed; delsp=yes

Hi Dan,
Project done been touched - we're committed to putting up something
with an upright axis in the wind....

Do you have any info about Urban Green Energy? Fellow we've been
talking with in NY is Ryan Gilchrist.

I've always thought it would be interesting if a client absolutely
insisted on VAWT's, no matter what I said, and we wouldn't be held
accountable for not dissuading them. The GC on this project has
offered to buy the turbines and carry the manufacturer's warranty with
the Navy, with us just responsible for the installation. I don't know
if it can get better than that. Monitoring and everything.

I just need to decide whether to give up the material sale. If we
managed to find a VAWT that could endure, and have a reasonable output
(it helps to get an additional 12?/kWh for production over net
metering in WA), we have several customers who would be interested,
even when fully informed about the low ROI compared to PV. These folks
just want to see SOME benefit to our long, windy winters and don't
have the moxy or money to put a VAWT up high. The turbine - and
company - just gotta last awhile.

Thanks,
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
NABCEP Certified PV Installer
ke...@whidbeysunwind.com
360.678.7131


On Oct 20, 2010, at 2:16 PM, Dan Fink wrote:

Kelly;

I would insist on a years worth of actual wind speed versus energy
output data performed by an unaffiliated third party, before even
touching this project with a 10-foot gin pole.

DAN FINK
Buckville Energy Consulting LLC

Kelly Keilwitz, Whidbey Sun & Wind wrote:
Wind wrenches,
We have a subcontract to install 30kW of VAWT, along with 30kW of
PV for the Navy. The Navy specified Helix Wind turbines, and is
adamant on sticking with VAWTs, although they may accept an
alternative. The GC we are working under is sufficiently scared of
Helix to look for a viable alternative. Are there any?!
The GC has done some research and wants to use the UGE-4K from
Urban Green Energy http://www.urbangreenenergy.com
It's an H-style lift machine that appears to have several European
certifications on safety, power performance, noise, and vibration.
Anyone know anything about these turbines or company? UGE's address
is NY. Roy?
Thanks,
-Kelly
Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
ke...@whidbeysunwind.com
360-678-7131
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




------------------------------

Message: 5
Date: Wed, 20 Oct 2010 17:25:00 -0600
From: Dan Fink <dan...@hughes.net>
To: "Kelly Keilwitz, Whidbey Sun & Wind" <ke...@whidbeysunwind.com>
Cc: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] VAWT recommendation
Message-ID: <4cbf7a4c.3000...@hughes.net>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed

Kelly;

I don't currently know of any product with which the words "VAWT" and
"last a while" can be used in the same sentence -- in terms of company longevity, number of units flying in the field, *or* turbine reliability
record.

DAN FINK
Buckville Energy Consulting LLC

Kelly Keilwitz, Whidbey Sun & Wind wrote:
Hi Dan,
Project done been touched - we're committed to putting up something with
an upright axis in the wind....

Do you have any info about Urban Green Energy? Fellow we've been talking
with in NY is Ryan Gilchrist.

I've always thought it would be interesting if a client absolutely
insisted on VAWT's, no matter what I said, and we wouldn't be held
accountable for not dissuading them. The GC on this project has offered to buy the turbines and carry the manufacturer's warranty with the Navy, with us just responsible for the installation. I don't know if it can
get better than that. Monitoring and everything.

I just need to decide whether to give up the material sale. If we
managed to find a VAWT that could endure, and have a reasonable output (it helps to get an additional 12?/kWh for production over net metering
in WA), we have several customers who would be interested, even when
fully informed about the low ROI compared to PV. These folks just want to see SOME benefit to our long, windy winters and don't have the moxy or money to put a VAWT up high. The turbine - and company - just gotta
last awhile.

Thanks,
-Kelly


------------------------------

Message: 6
Date: Wed, 20 Oct 2010 18:43:20 -0500
From: "North Texas Renewable Energy Inc" <nt...@1scom.net>
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Mounting Enphase when using S-5-PV Clamps
Message-ID: <gpejjfplcdgedngdfoofkegfcjaa.nt...@1scom.net>
Content-Type: text/plain; charset="windows-1252"

Benn
just bear in mind that any adjustment of the module height, must be
performed by turning a jam nut under the S5-PV clamps mounting surface and will need to be done from below using an open-end wrench! If the ribs are
pretty level that may not be such a chore. But I've seen some pretty
unlevel
metal ribs on older roofs.
Carry along a 10-12 foot rail section for a straightedge to get the
heights
on the money before you start to clamp modules.

Jim Duncan
North Texas Renewable Energy
 -----Original Message-----
 From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]on Behalf Of benn
kilburn
 Sent: Wednesday, October 20, 2010 5:18 PM
 To: Wrenches
 Subject: Re: [RE-wrenches] Mounting Enphase when using S-5-PV Clamps


 Not a lot of you guys in the field today 'eh?  I was just checking a
spec
on my laptop and noticed i had a wireless signal and a mailbox full of
great
feedback, thanks again everyone!!!


I'll go over all the details from everyone a little more when i'm done
on
site for the day. For a few of you i just wanted to show you this link to the S-5-PV clamp, which is different from just the S-5! clamp > Click
here
to learn more. < The S-5-PV does not need rails, the mod frames sit on
the
'mounting disc' which can accommodate one or two modules. BUT, with the Enphase system, this leave no where to mount the inverters. Bill made a
good point; save this mounting method for string inverter systems.
We are now planning this project using just the S-5 clamp/L-foot/ rail
system.  No problems.


 Back at 'er!

 benn
 DayStar Renewable Energy Inc.
 b...@daystarsolar.ca
 780-906-7807
 HAVE A SUNNY DAY

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/975644fc/attachment-0001.htm >

------------------------------

Message: 7
Date: Wed, 20 Oct 2010 16:49:58 -0700
From: "Kelly Keilwitz, Whidbey Sun & Wind" <ke...@whidbeysunwind.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] VAWT recommendation
Message-ID: <08f54956-ed41-480e-9324-74bef8378...@whidbeysunwind.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed; delsp=yes

Yeah, me either...... (sigh)...

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
NABCEP Certified PV Installer
ke...@whidbeysunwind.com
360.678.7131

On Oct 20, 2010, at 4:25 PM, Dan Fink wrote:

Kelly;

I don't currently know of any product with which the words "VAWT"
and "last a while" can be used in the same sentence -- in terms of
company longevity, number of units flying in the field, *or* turbine
reliability record.

DAN FINK
Buckville Energy Consulting LLC

Kelly Keilwitz, Whidbey Sun & Wind wrote:
Hi Dan,
Project done been touched - we're committed to putting up something
with an upright axis in the wind....
Do you have any info about Urban Green Energy? Fellow we've been
talking with in NY is Ryan Gilchrist.
I've always thought it would be interesting if a client absolutely
insisted on VAWT's, no matter what I said, and we wouldn't be held
accountable for not dissuading them. The GC on this project has
offered to buy the turbines and carry the manufacturer's warranty
with the Navy, with us just responsible for the installation. I
don't know if it can get better than that. Monitoring and everything.
I just need to decide whether to give up the material sale. If we
managed to find a VAWT that could endure, and have a reasonable
output (it helps to get an additional 12?/kWh for production over
net metering in WA), we have several customers who would be
interested, even when fully informed about the low ROI compared to
PV. These folks just want to see SOME benefit to our long, windy
winters and don't have the moxy or money to put a VAWT up high. The
turbine - and company - just gotta last awhile.
Thanks,
-Kelly



------------------------------

Message: 8
Date: Wed, 20 Oct 2010 17:01:32 -0700 (PDT)
From: Exeltech <exelt...@yahoo.com>
To: gilliga...@gmail.com, RE-wrenches
        <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Inverter 1741 Listing Process
Message-ID: <212162.45991...@web113418.mail.gq1.yahoo.com>
Content-Type: text/plain; charset="utf-8"

Matt et. al.,

IEEE 1547, 7.1.1 states "The commissioning test shall be performed to
verify that the completed and installed ICS meets the requirements of IEEE
Std 1547."

Verification on the grid-tie equipment has been done for you by the NRTL as part of the UL1741 test procedure, which, as Matt pointed out, has IEEE
1547 as a subset.


I refer you back to page iii at the front of IEEE 1547.1, which states: "IEEE Std 1547.1 provides conformance test procedures to establish and verify compliance with the requirements of IEEE Std 1547.? When applied, the IEEE 1547.1 test procedures can provide a means for manufacturers, utilities, or independent testing agencies to confirm the suitability of any given interconnection system (ICS) or component intended for the use
in the interconnection of DR ("distributed resources") with the EPS
("electric power system").? Such certification can lead to the ready
acceptance of confirmed equipment as suitable for use in the intended
service by the parties concerned."

[Note: Quoted items in parentheses are mine for clarification purposes.]

Also...
In IEEE 1547.1 Section 6.4, "Documentation" refers to the
documentation we as manufacturers are required to provide with each unit to the NRTL for audit purposes.? The NRTL shows up unannounced, and may
review our test records at any time.? The documentation mentioned in
IEEE 1547 is part of our audit trail.? "Production test documentation"
is not included with units that leave the factory.

So .. in plain English .. none of the "Commissioning Tests" are required on site of any UL1741-certified inverter.? This is not to say an AHJ or
utility won't ever ask for them, but if it happened, that would be an
AHJ/utility-specific issue.

My $0.02+ from the manufacturer's side of the fence...


Dan



--- On Wed, 10/20/10, Matt Lafferty <gilliga...@gmail.com> wrote:

From: Matt Lafferty <gilliga...@gmail.com>
Subject: Re: [RE-wrenches] Inverter 1741 Listing Process
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
Date: Wednesday, October 20, 2010, 2:20 PM




Thanks Guys,
?
Here's an update for anyone who cares.
?
The specifics I was looking for?are included in IEEE
1547.1, which is inherently included in UL 1741. In other words, since
2007, if
you have an inverter listed to UL 1741, it must also meet (by
certification) the
requirements of IEEE 1547 and 1547.1. In fact, the sections of UL 1741
that
formerly applied to the Utility Compatibility functions have been removed.
Voido. They are now replaced by IEEE 1547 & IEEE 1547.1.

?
IEEE 1547.1 is clear and precise about the production test
requirements I was looking for. UL 1741 is weak on the issue. In general,
utility companies rely on IEEE documents and requirements for their
guidance. I
see why some of them require field verification of the non-islanding
function by
flipping the AC switch off with the inverter running... Well, not exactly.
Technically, the non-islanding function is something else. The
"Cease-to-energize" function is what they are actually verifying in the
field.
Here's a short rundown on the issue....
?
IEEE 1547.1 (Clause 6; Production Tests) requires production
tests for response to abnormal voltage, response to abnormal frequency,
and
synchronization. Combined, these would constitute production testing that
confirms the non-islanding functions that are Type tested on a sample
unit.
And there's more. This section also requires that the documentation
of these production tests be provided with the equipment.
?
IEEE 1547.1 (Clause 7; Commissioning) requires some
verification and testing steps. These are allowed to be performed by a
qualified
person and the utility may require that they witness the process (at
their option). Inherent to this section is a requirement that
there be a commissioning report generated which contains data related to
the
process. "A commissioning test report shall be produced and shall contain
the results of all tests and a listing of the final ICS
settings."
?
The required steps involved in Commissioning
include:?Verification and Inspection, Identifying any required Type and Production tests that were not performed and performing them in the field;
Unintentional Islanding functionality test; Cease-to-energize
functionality
test; Documentation of revised settings.
?

Understand that all of these steps are REQUIRED AS PART OF THE
COMMISSIONING PROCESS, per IEEE 1547.1.
?
My focus is primarily on the Commissioning procedure... I'll skip the
inspection and verification?steps for this
post.
?
Note that Clause
7.3 of?the Commissioning section requires field performance of any Type or Production tests that have not been performed. When the manufacturer fails
to
include the Documentation of Production Tests with their product, the
commissioning technician has no choice but to do them in the
field.
?
(NOTE TO INVERTER MFRS: INCLUDE CLEAR DOCUMENTATION OF YOUR
PRODUCTION TESTS WITH EACH INVERTER, PER IEEE 1547.1 Clause 6.4; NOTE TO
INSTALLERS: HAVE THIS DOCUMENTATION HANDY AND LEAVE IT WITH THE
INVERTER.)
?
Clause 7.4 is the Unintentional Islanding functionality test.
If the unit is connected to the grid via reverse-power
or?minimum-power?protection equipment (commonly referred to as
non-export or zero-export; relatively rare) instructions are given for
testing.
This test is?waived if the inverter is certified to Clause 5.7, the
Type test for Unintentional Islanding. (Check) If the unit is not
certified to
5.7 and not connected via zero-export protection equipment, this function
is to
be tested according to procedures provided by the integrator or the
manufacturer. UL 1741 Listed inverters should be certified to Clause?5.7,
which makes them eligible for the waiver.
?
Clause 7.5 is the
Cease-to-energize functionality test. This tests that the inverter does
not
energize the output (AC) terminals on loss of grid AC. It also checks that
the
restart/reconnect time delay (5-minute wait) functions as required. The
test is
simple. Run the inverter at any power level and open the ungrounded AC
phase
conductors. Verify that the output terminals of the inverter are not
energized.
Apply AC power. Verify that the unit waits the required amount of time to
reconnect.
?
There are two important sentences in this Clause to know
about. The first is that "An ICS that meets the requirement so 5.9
(open-phase type test) and 7.4.1 (zero-export) satisfies the requirements
of
this subclause." This means that a UL 1741 Listed inverter interconnected
via zero-export equipment is exempt from this test.
?
The second sentence to know about is this one: "The
following procedure may be adjusted dependent on an agreement between the
area
EPS authority (electric utility) and the system installer." This means that, every time the utility does not require you to test this function,
they
are agreeing to "adjust" this procedure, even if they don't tell you they
are.
You are getting a free pass.
?
Let me repeat that another way... IEEE 1547.1 REQUIRES that
this test be done unless the above-mentioned exemptions are met. As an
installer, you must be prepared for and expect to do this test.

?
Nowhere in the Commissioning section of IEEE 1547.1 does it
exempt performing the Commissioning steps or producing?the Commissioning
test report.
?
I am of the strong opinion that having the manufacturer's
Production Test Documentation on-hand will go a long way toward gaining
the?utility's acceptance of the system without performing
the?Cease-to-energize functionality test. I believe that most of our
modern
inverters will meet one of the exceptions to the Unintentional Islanding
functionality test. I believe that it is best practice to perform
comprehensive
commissioning on all systems, and record the relevant data. I have always
found
that doing this and having your documentation together gains respect from
AHJs
and utility inspectors. I believe that by doing this, we demonstrate
professionalism and responsibility. Working with utilities in a manner
that
demonstrates professional, knowledgeable, and responsible behavior can
only
benefit our respective organizations.
?
Happy commissioning!
?
Matt
Lafferty


From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Exeltech
Sent: Tuesday, October 19, 2010 12:20 PM
To:
RE-wrenches
Subject: Re: [RE-wrenches] Inverter 1741 Listing
Process






   boB covered the main points perfectly.

Manufacturers
     of UL-certified products are subject to unannounced spot-checks
several
times a year by the issuing NTRL to verify the products coming off
the
production line are absolutely identical to the products submitted
for UL
     testing.? Any major deviation in the production units from
lab-tested
units can result in immediate de-certification and possible recall
of any
     affected product(s).? "Major" in this case could be different
software, mechanical changes, or a substitution of any components
that
     affect safety or unit operation in any manner with unauthorized
components
     .. for openers.

By the way .. for anyone who's not met boB in
person .. I had the good fortune to do so at the Midwest Renewable
Energy
     Fair in Wisconsin this past June.? Great
     guy.

Dan


--- On Tue, 10/19/10, boB Gudgel
     <b...@midnitesolar.com> wrote:


From:
       boB Gudgel <b...@midnitesolar.com>
Subject: Re: [RE-wrenches]
       Inverter 1741 Listing Process
To: gilliga...@gmail.com, "RE-wrenches"
       <re-wrenches@lists.re-wrenches.org>
Date: Tuesday, October 19,
       2010, 12:42 AM


       On 10/18/2010 9:53 PM, Matt Lafferty wrote:

         Thanks for the info Dan and boB.
         ?
         What production tests required to maintain listing? Do you
         happen to know if there is a different regimen for micro vs
string vs
         central inverters?

You mean, a
difference between the two when UL, ETL, CSA comes by for their
pop
       inspection ??

Off hand, I don't? see why one inverter would
       be given any different kind of attention than the other
type.?
The UL/ETL followup inspections are basically to make sure you are
       following the proper
manufacturing and testing processes such as,
       software version, verification that you are using
UL recognized?
       sources of parts and materials, hi-potting at the correct
voltages,
       etc.


They are both grid-tie inverters so the testing
       processes are very similar.

?I'm sure that Dan will pick up
       on anything? important that I forgot.

boB




         ?
         I'm working on developing?a detailed commissioning
         procedure. Detailed yet generic. There will be at least two
versions
for inverters. One for string and one for central. In my book,
central
inverters have re-combiners (standalone or integral) and string inverters don't. I'm trying to understand which functions are
tested in the
factory on every unit so I can avoid unnecessary duplication by
the
         commissioning people.
         ?
         Thanks in advance for any light you can shed on the
         subject!
         ?
         Matt
         Lafferty


         From: re-wrenches-boun...@lists.re-wrenches.org
         [mailto:re-wrenches-boun...@lists.re-wrenches.org]
         On Behalf Of Exeltech
Sent: Monday, October 11, 2010
         10:04 AM
To: RE-wrenches
Subject: Re:
         [RE-wrenches] Inverter 1741 Listing Process





             Matt,

The 5-minute delay is verified in
the group of inverters sent to the test laboratory.? Then, as long as the software and hardware don't change, it's
presumed
               the delay in all production units meets the value(s)
measured in
               the tested units.

An alteration in either hardware OR
software can result in a unit being required to completely
               re-test (as Bob pointed out).? NRTLs get copies of the
source code and can and do periodically compare their copy
as
               submitted with the original test units to the software
being
programmed into the inverters during production to verify
it's
               the same.

NRTLs conduct unannounced "field audits" by
simply showing up on site and randomly selecting various
aspects
               of the product for verification -- including the
               software.

The overall UL1741 certification process is
               extremely complex, very time consuming, and quite
               expensive.


Dan



--- On Fri, 10/8/10,
               boB Gudgel <b...@midnitesolar.com>
               wrote:


From:
                 boB Gudgel <b...@midnitesolar.com>
Subject:
                 Re: [RE-wrenches] Inverter 1741 Listing Process
To: gilliga...@gmail.com,
                 "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date:
                 Friday, October 8, 2010, 9:26 PM


                 On 10/8/2010 6:04 PM, Matt
                 Lafferty wrote:

                   Hola Wrenches,
                   ?
                   Does anybody know off the top of their
                   head if the "5-minute-wait-to-interconnect"
                   function is tested on 100% of inverters produced?
(i.e.
every?single inverter is tested with AC & DC within
                   the start parameters of the unit for at least 5
                   minutes)
                   ?
                   Thanks!
                   ?
                   Matt
                 Lafferty
Good
                 question.? I bet it's not 100% tested because if the
                 software does not
change, then they may just not wait the
                 extra 5 minutes in order to save money on testing.

Or,
                 maybe they do a random sampling for this
                 test.

Theoretically, it shouldn't matter as long as the
                 software does not change
and the hardware is tested enough
                 in other ways, like, timers and clocks etc.

BTW,
                 Nowadays, there are two options for manufacturers of
grid
                 interactive inverters....

And the UL spec has gotten
                 more stringent.

One option? is that you have to
                 have? the? code (software) blessed by the NRTL in a
                 separate process (another UL specification, (UL 1998
?Software
                 in Programmable Components")

OR, if they don't go for
that option, then if software changes need to be done to
the
inverter, the inverter must (technically) go through the
                 UL1741 listing process all over
               again.

boB
       ?

-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/906d8a05/attachment-0001.htm >

------------------------------

Message: 9
Date: Wed, 20 Oct 2010 19:10:00 -0500
From: "North Texas Renewable Energy Inc" <nt...@1scom.net>
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <gpejjfplcdgedngdfoofoeggcjaa.nt...@1scom.net>
Content-Type: text/plain; charset="us-ascii"

MessageAfter re-reading your original letter Chris, it sounds like the
roof
makeover hasn't happened yet. If that's the case suggest to the owner
that,
based on the 100 years or so of combined professional experience of the PV installer community, he should not use the engineered rafters or the 1/2"
decking if he's wanting PV on top.
Pull out a copy of the International Building Code and show him.

not a roofer,

Jim Duncan

Dear Wrenches
have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those (sort of) particle board I-beams covered with 1/2" plywood (and shingles). What's the best metal roofing you could suggest--and would you beef up the
wood to lag into?
     Thanks for all your input.
     Chris Daum
     Oasis Montana Inc.
     406-777-4309
     406-777-0830 fax
     _______________________________________________
     List sponsored by Home Power magazine

     List Address: RE-wrenches@lists.re-wrenches.org

     Options & settings:
     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

     List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

     List rules & etiquette:
     www.re-wrenches.org/etiquette.htm

     Check out participant bios:
     www.members.re-wrenches.org



-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/385f2e44/attachment-0001.htm >

------------------------------

Message: 10
Date: Wed, 20 Oct 2010 18:50:32 -0600
From: "Chris Daum" <ch...@oasismontana.com>
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <1287622268_1250...@gwa5>
Content-Type: text/plain; charset="us-ascii"

You are correct -- and there is a strong possibility of adding another
layer
(1/2" or 3/4") of roofing material under the new metal roof. High wind
area
is a consideration, and I don't think those fake I-beams are meaty enough
to
lag into.  Hence I request your input!

--Chris @ the Oasis Montana

 _____

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of North
Texas
Renewable Energy Inc
Sent: Wednesday, October 20, 2010 6:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] The perfect solar ready roof


After re-reading your original letter Chris, it sounds like the roof
makeover hasn't happened yet. If that's the case suggest to the owner
that,
based on the 100 years or so of combined professional experience of the PV installer community, he should not use the engineered rafters or the 1/2"
decking if he's wanting PV on top.
Pull out a copy of the International Building Code and show him.

not a roofer,

Jim Duncan

Dear Wrenches
have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those (sort of) particle board I-beams covered with 1/2" plywood (and shingles). What's the best metal roofing you could suggest--and would you beef up the
wood to lag into?


Thanks for all your input.


Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>




-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101020/323f05b3/attachment-0001.htm >

------------------------------

Message: 11
Date: 20 Oct 2010 20:58:59 -0400
From: richard.l.rat...@valley.net (Richard L Ratico)
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <136086...@retriever.valley.net>
Content-Type: text/plain

Chris,

You've probably already considered and rejected this... Unisolar PVL
modules on
standing seam roofing. Solves the structure & wind problems. Goes fast if installed on the pans before they go on the roof. Price is pretty good per
watt
now.
Can't beat the look. Made in USA. I think the only downside is you may not
have
enough area to place 5kW.

I bet it's getting cold in Montana. You could stick the modules on the
pans in a
heated space somewhere. This would really cut down your time and exposure
on the
roof.

Dick Ratico
Solarwind Electric



--- You wrote:
Dear Wrenches
have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those (sort of) particle board I-beams covered with 1/2" plywood (and shingles). What's the best metal roofing you could suggest--and would you beef up the
wood to lag into?
     Thanks for all your input.
     Chris Daum
     Oasis Montana Inc.
     406-777-4309
     406-777-0830 fax
--- end of quote ---


------------------------------

Message: 12
Date: Wed, 20 Oct 2010 19:29:33 -0600
From: "Chris Daum" <ch...@oasismontana.com>
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <1287624608_1251...@gwa5>
Content-Type: text/plain;       charset="us-ascii"

Hi Dick:

Nope, not just high wind area, but the site gets a real bashing of hail at least once every 3 to 4 years (like quarter sized hail at 60 - 80 mph) --
so
I will pass on the plasticky amorphous stuff, thank you, although yes,
they
do look nice (til they get those whitish translucent spots from hail). There's room for about a 5.5KW array of some decent modules (read: Sanyos
or
some other high efficient modules). I just think we need another layer of
roofing material; we'll need 16 sheets of some kinda plywood.  I am
leaning
more and more in that direction.....

But I really do appreciate all your thoughts! And by the way, right NOW,
sunny day time temps are near 70.....  Nights are a chilly 35.....

Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard L
Ratico
Sent: Wednesday, October 20, 2010 6:59 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] The perfect solar ready roof

Chris,

You've probably already considered and rejected this... Unisolar PVL
modules
on standing seam roofing. Solves the structure & wind problems. Goes fast
if
installed on the pans before they go on the roof. Price is pretty good per
watt now.
Can't beat the look. Made in USA. I think the only downside is you may not
have enough area to place 5kW.

I bet it's getting cold in Montana. You could stick the modules on the
pans
in a heated space somewhere. This would really cut down your time and
exposure on the roof.

Dick Ratico
Solarwind Electric



--- You wrote:
Dear Wrenches
have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those (sort of) particle board I-beams covered with 1/2" plywood (and shingles). What's the best metal roofing you could suggest--and would you beef up the
wood to lag into?
     Thanks for all your input.
     Chris Daum
     Oasis Montana Inc.
     406-777-4309
     406-777-0830 fax
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





------------------------------

Message: 13
Date: Wed, 20 Oct 2010 21:31:53 -0700 (PDT)
From: Darryl Thayer <daryl_so...@yahoo.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] VAWT recommendation
Message-ID: <284147.86340...@web51901.mail.re2.yahoo.com>
Content-Type: text/plain; charset=iso-8859-1

I have been known to be an idiot, but put it up for the labor IF you can be sure you are done. I have tested some, and not only did they not last,
they did not produce.

--- On Wed, 10/20/10, Kelly Keilwitz, Whidbey Sun & Wind
<ke...@whidbeysunwind.com> wrote:

From: Kelly Keilwitz, Whidbey Sun & Wind <ke...@whidbeysunwind.com>
Subject: Re: [RE-wrenches] VAWT recommendation
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Wednesday, October 20, 2010, 6:49 PM
Yeah, me either...... (sigh)...

Kelly Keilwitz, P.E.
Whidbey Sun & Wind
Renewable Energy Systems
NABCEP Certified PV Installer
ke...@whidbeysunwind.com
360.678.7131

On Oct 20, 2010, at 4:25 PM, Dan Fink wrote:

Kelly;

I don't currently know of any product with which the
words "VAWT" and "last a while" can be used in the same
sentence -- in terms of company longevity, number of units
flying in the field, *or* turbine reliability record.

DAN FINK
Buckville Energy Consulting LLC

Kelly Keilwitz, Whidbey Sun & Wind wrote:
Hi Dan,
Project done been touched - we're committed to
putting up something with an upright axis in the wind....
Do you have any info about Urban Green Energy?
Fellow we've been talking with in NY is Ryan Gilchrist.
I've always thought it would be interesting if a
client absolutely insisted on VAWT's, no matter what I said,
and we wouldn't be held accountable for not dissuading them.
The GC on this project has offered to buy the turbines and
carry the manufacturer's warranty with the Navy, with us
just responsible for the installation. I don't know if it
can get better than that. Monitoring and everything.
I just need to decide whether to give up the
material sale. If we managed to find a VAWT that could
endure, and have a reasonable output (it helps to get an
additional 12?/kWh for production over net metering in WA),
we have several customers who would be interested, even when
fully informed about the low ROI compared to PV. These folks
just want to see SOME benefit to our long, windy winters and
don't have the moxy or money to put a VAWT up high. The
turbine - and company - just gotta last awhile.
Thanks,
-Kelly

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org







------------------------------

Message: 14
Date: Thu, 21 Oct 2010 01:55:30 -0600
From: benn kilburn <b...@daystarsolar.ca>
To: Wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] The perfect solar ready roof
Message-ID: <col121-w64a4d6d7499097655528e0ad...@phx.gbl>
Content-Type: text/plain; charset="iso-8859-1"


chris,don't forget to make sure that the existing roof structure is
engineered to support the added weight of the extra layer of plywood, as
well as the racking/modules.
benn
DayStar Renewable Energy Inc. b...@daystarsolar.ca780-906-7807 HAVE A
SUNNY DAY







From: ch...@oasismontana.com
To: re-wrenches@lists.re-wrenches.org
Date: Wed, 20 Oct 2010 19:29:33 -0600
Subject: Re: [RE-wrenches] The perfect solar ready roof

Hi Dick:

Nope, not just high wind area, but the site gets a real bashing of hail
at
least once every 3 to 4 years (like quarter sized hail at 60 - 80 mph)
-- so
I will pass on the plasticky amorphous stuff, thank you, although yes,
they
do look nice (til they get those whitish translucent spots from hail).
There's room for about a 5.5KW array of some decent modules (read:
Sanyos or
some other high efficient modules). I just think we need another layer
of
roofing material; we'll need 16 sheets of some kinda plywood.  I am
leaning
more and more in that direction.....

But I really do appreciate all your thoughts!  And by the way, right
NOW,
sunny day time temps are near 70.....  Nights are a chilly 35.....

Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard
L
Ratico
Sent: Wednesday, October 20, 2010 6:59 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] The perfect solar ready roof

Chris,

You've probably already considered and rejected this... Unisolar PVL
modules
on standing seam roofing. Solves the structure & wind problems. Goes
fast if
installed on the pans before they go on the roof. Price is pretty good
per
watt now.
Can't beat the look. Made in USA. I think the only downside is you may
not
have enough area to place 5kW.

I bet it's getting cold in Montana. You could stick the modules on the
pans
in a heated space somewhere. This would really cut down your time and
exposure on the roof.

Dick Ratico
Solarwind Electric



--- You wrote:
Dear Wrenches
have a composite (shingle) roof at hand, and the owner wants to upgrade
it
to a metal roof and install a 5kw+ array on it. The rafters are those
(sort of) particle board I-beams covered with 1/2" plywood (and
shingles).
What's the best metal roofing you could suggest--and would you beef up
the
wood to lag into?
     Thanks for all your input.
     Chris Daum
     Oasis Montana Inc.
     406-777-4309
     406-777-0830 fax
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101021/8c4aeefd/attachment.htm >

------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



End of RE-wrenches Digest, Vol 3, Issue 585
*******************************************



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to