On 10/8/2010 6:04 PM, Matt Lafferty wrote:
Hola Wrenches,
Does anybody know off the top of their head if the /"5-minute-wait-to-interconnect"/ function is tested on 100% of inverters produced? /(i.e. every single inverter is tested with AC & DC within the start parameters of the unit for at least 5 minutes)/
Thanks!
Matt Lafferty

Good question.  I bet it's not 100% tested because if the software does not
change, then they may just not wait the extra 5 minutes in order to save money on testing.
Or, maybe they do a random sampling for this test.

Theoretically, it shouldn't matter as long as the software does not change
and the hardware is tested enough in other ways, like, timers and clocks etc.


BTW, Nowadays, there are two options for manufacturers of grid interactive inverters....
And the UL spec has gotten more stringent.

One option is that you have to have the code (software) blessed by the NRTL in a separate process (another UL specification, (UL 1998 --Software in Programmable Components")

OR, if they don't go for that option, then if software changes need to be done to the inverter, the inverter must (technically) go through the UL1741 listing process all over
again.

boB


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to