All,

 

Transformerless inverters are simply a subset of ungrounded or resistively 
grounded PV systems covered by the NEC in 690.35 since the 2005 code cycle. 
Power-One has been marketing their ungrounded inverter in the U.S. for several 
years now. It was listed by CSA. The requirements for ungrounded systems in 
690.35 are as follows:

 

•          “Photovoltaic power systems shall be permitted to operate with 
ungrounded photovoltaic source and output circuits where the system complies 
with 690.35(A) through 690.35(G).

−      (A) Disconnects. All photovoltaic source and output circuit conductors 
shall have disconnects complying with 690, Part III.

−      (B) Overcurrent Protection. All photovoltaic source and output circuit 
conductors shall have overcurrent protection complying with 690.9.

−      (C) Ground-Fault Protection. All photovoltaic source and output circuits 
shall be provided with a ground-fault protection device or system that complies 
with (1) through (3):

•          (1) Detects a ground fault.

•          (2) Indicates that a ground fault has occurred

•          (3) Automatically disconnects all conductors or causes the inverter 
or charge controller connected to the faulted circuit to automatically cease 
supplying power to output circuits.

−      (D) The photovoltaic source and output conductors shall consist of the 
following:

−      (1) Nonmetallic jacketed multiconductor cables

−      (2) Conductors installed in raceways, or

−      (3) Conductors listed and identified as Photovoltaic (PV) Wire installed 
as exposed, single conductors.

−      (E) The photovoltaic power system direct-current circuits shall be 
permitted to be used with ungrounded battery systems complying with 690.71(G).

−      (F) The photovoltaic power source shall be labeled with the following 
warning at each junction box, combiner box, disconnect, and device where the 
ungrounded circuits may be exposed during service:

WARNING

ELECTRIC SHOCK HAZARD

THE DC CIRCUIT CONDUCTORS OF THIS

PHOTOVOLTAIC POWER SYSTEM ARE

UNGROUNDED AND MAY BE ENERGIZED

WITH RESPECT TO GROUND DUE TO

LEAKAGE PATHS AND/OR GROUND FAULTS.

−      (G) The inverters or charge controllers used in systems with ungrounded 
photovoltaic source and output circuits shall be listed for the purpose.

 

We now have several products newly on the market to include on the list such as 
the SMA and Exeltech products. Ungrounding the array requires additional fusing 
and disconnects, but the most significant difference is that the module wiring 
and all external cable must be PV Wire/Cable. Therefore only modules with PV 
Wire/Cable can be used in these systems. You must confirm from the manufacturer 
that they have made the switch. Hopefully all manufacturers will be installing 
PV Wire/Cable soon so that this will not be a problem anymore.

 

It is a good call to use up your USE-2 and order PV Wire/Cable from now on.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Friday, October 01, 2010 6:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Tranformless inverter

 


Transformerless grid-tie inverters are permitted under the National Electric 
Code as of 2008.  The Nationally Recognized Testing Laboratories (UL, 
ETL/Intertek, CSA, etc.) took a while to develop the testing procedures for 
testing to UL1741, which was the basis for most of the delay.

SMA isn't the only company with transformerless grid-tie inverters.  I know of 
one American manufacturer with transformerless models on the market as well.

Transformerless inverters are smaller, much lighter, and tend to be more 
efficient than transformer-based units.  No transformer also means lower 
product cost, and less shipping expense.  Win-win-win.


Dan


--- On Fri, 10/1/10, Drake <drake.chamber...@redwoodalliance.org> wrote:


From: Drake <drake.chamber...@redwoodalliance.org>
Subject: Re: [RE-wrenches] Tranformless inverter
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Friday, October 1, 2010, 6:58 AM

I also received this advertisement.  Previously I had investigated the smaller 
SMA transformerless inverters, and was told that this type would not be allowed 
in the US until the 2011 code.  Has the ban been lifted?



At 12:52 AM 9/29/2010, you wrote:



Wrenches:

I received an advertisement from a distributor that SMA is now shipping 8, 9 
and 10 KW transformerless inverters.  Don't these require double insulated PV 
wiring and no connection  to ground on the AC side? It's been too long since 
this subject last crossed my desk and I want to refresh my memory on the 
specifics.

William Miller


Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com <http://millersolar.com/> 
License No. C-10-773985

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to