Andrew:

You make a very good point in 2) below, however there is one step missing: If a ground fault is occurring, the technician will eventually need to look under modules to find the fault. This is the reason the top-down clips will be loosened. If the module is grounded with #6 wire, the wire will prevent the module from being lifted. Therefore, the lug will also be loosened, un-grounding the module -- creating the unsafe condition you described.

WEEB clip or WEEB lug, the technician dies.

Should we invent a WEEB jumper cable to maintain module bond while the modules are being lifted?

William Miller



At 07:44 PM 9/13/2010, you wrote:



2) My biggest concern with the WEEB Clip is that the moment a top-clamp is loosened the module is no longer grounded!!! To me that is not a good grounding method. Mr Wiley is obviously a talented inventor and he makes a strong argument for the quality of the bond that the WEEB Clip provides when the clip is installed properly and all mounting hardware is properly torqued. What I don't understand is the argument that this is as safe of a product as a properly installed outdoor rated lug for the service tech who has to work on that array.


A tin-plated copper lug with a stainless steel set screw will last. A service tech working on a faulted array that was grounded with WEEB Clips might not.



Andrew Truitt
Free agent
Golden, CO.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to