Kent:

Your comments below are right on the mark and well said.

William Miller





At 09:43 PM 9/7/2010, you wrote:
Matt,

There is a word on the KLKD time delay chart you referenced that is hiding a very important fact. Those are "average" curves. To illustrate what that means take a look at the time delay curve for the <http://www.cbi-electric.com/show_pictures.php?title=Product%20Curves&path=/curves_products/6>CBI breaker commonly used for battery charging systems. There is a gray area that extends from 105% to 130% of rating. Over that range, the breaker may or may not trip. While not shown on the KLKD fuse time delay chart that you referenced, a very similar gray zone exists. These fuses and breakers are simply not precise enough devices to distinguish between Imp and Isc at STC in the best of conditions.

if you did manage to select a fuse that would blow at Isc but not at Imp, it still wouldn't blow during a short if the irradiance was 800 W/sq m. An arcing fault at 800 W/sq m can still burn a big hole. It simply isn't possible to provide good fault protection for PV systems with fuses. What's needed is a ground fault protector/arc fault protector that is located in the combiner box. Until that exists, the feeder between the combiner and inverter needs to be considered an unfused conductor.

Kent Osterberg
Blue Mountain Solar

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to