This May 2010 UL/NFPA report "Fire Fighter Safety and Emergency Response for 
Solar Power Systems" shows  eave-to-ridge solar arrays and has a lot of good 
information for designers. See 
http://www.nfpa.org/assets/files/PDF/Research/FFTacticsSolarPower.pdf

  ----- Original Message ----- 
  From: Mick Abraham 
  To: RE-wrenches 
  Sent: Thursday, August 26, 2010 5:53 PM
  Subject: Re: [RE-wrenches] Tight roof layout questions: edge walkway 
requirements & "small gap" hardware options


  The Wrench List participants have again responded with aplomb. Thanks to all 
for the dozen or so replies. My takeaway from this is that I need to send my 
roof layouts to the nearby fire department...it's another "authority having 
jurisdiction" situation.


  I received the below mail "off list" from a fire captain in San Jose. He 
cannot post to the List so he asked me to post on his behalf. Moderator Michael 
approved, so Matt Paiss' remarks are copied below. 


  Jolliness,  
  Mick Abraham, Proprietor 
  www.abrahamsolar.com
  Voice: 970-731-4675


    Mick,
    I wanted to reply to your post.  As a firefighter, and an instructor of PV 
safety for the fire service like Dan Fink, I would like to take a moment to 
expand on what Dan was eluding to.  Firefighters will not always look at an 
edge-to-edge array and decide to "Let it burn" just based on the array size.  
We will take into account the size of the fire, the involvement of the actual 
structural members, and the potential life risk within the structure before any 
tactical strategy is implemented.  I have written off buildings just based on 
wind, or available water supply.
    What a setback (the term being used for walkways) allows is primarily for 
access to a roof, or rapid egress off a roof when the fire gets out of control, 
not necessarily for cutting a hole.  I teach firefighters to vent on the other 
side of the ridge from the array.  There is no time to remove modules, and 
while micro-inverters definitely address the safety issues of a 600vdc string, 
they do not address access or egress.  I am not going to recommend that ANY 
firefighter tear off a module to vent a roof because he "thinks" a 
micro-inverter is present.
    I realize that these new codes are more restrictive, but even wind load 
zones recommend against edge-to-edge installs.  There will be some latitude in 
the fire codes for setbacks,  so I recommend building a good relationship with 
your local AHJ's.  One way of doing this is by demonstrating safe, high quality 
installs.  I have seen too many wire-ties holding up PV wire that will be 
rubbing against comp shingles for a decade.  How confident are you that that 
will not be a problem?
    Regards,
    Matt Paiss
    Matthew Paiss, Fire Captain
    San Jose Fire Department
    170 W. San Carlos St.
    San Jose, CA 95113
    (831) 566-3057 cell


  On Thu, Aug 26, 2010 at 12:45 AM, Philip Boutelle <philboute...@gmail.com> 
wrote:

    Just to clarify what is and isn't law in California: 
    the final draft guidelines developed and adopted by Cal Fire are 
guidelines, not law, unless the local fire/AHJ has adopted them or parts of 
them into local ordinances. I have heard that in Southern Cal, those guidelines 
have been adopted all over the place already, but not so in the rest of the 
state.... yet. I think the guideline was officially incorporated into the next 
NEC/NFPA cycle, so it will be law pretty soon. Bill Brooks could probably 
confirm here on future adoption.
    Not that any of this helps your Atlanta install....


    -Phil Boutelle
    Real Goods Solar  


    On Wed, Aug 25, 2010 at 12:38 PM, Max Balchowsky <m...@seesolar.com> wrote:

      Mick, here in California the fire department in the various agencies has 
the final say on clearances. There is a very clear cut standard in place for 
the state, but we have been successful a few times in getting allowances to 
vary due to various site conditions. A call to the local AHJ is the place to 
start. In the early days of our installations (mid 1990's) we used power strut 
and bolted panels directly to the rails. A lot slower but no gaps between 
panels. We went from there to designing our own "T" clamps. There wasn't as 
many choices then for mounting hardware. 


      Max Balchowsky
      Design Engineer
      SEE Systems
      1048 Irvine Ave Suite 217
      Newport Beach, Ca. 92660
      760-403-6810





--------------------------------------------------------------------------
      From: Brian Teitelbaum <bteitelb...@aeesolar.com>
      To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
      Sent: Wed, August 25, 2010 11:40:04 AM
      Subject: Re: [RE-wrenches] Tight roof layout questions: edge walkway 
requirements & "small gap" hardware options



      Hi Mick,



      To answer part of your post, the DPW Power Rail mid-clamps give you a 
3/8” gap between modules, and the SnapNrack mids give you a 1/2"  gap.



      I doubt if that will give you much of a walkway though….



      Brian Teitelbaum

      AEE Solar





      From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mick Abraham
      Sent: Wednesday, August 25, 2010 11:09 AM
      To: RE-wrenches
      Subject: [RE-wrenches] Tight roof layout questions: edge walkway 
requirements & "small gap" hardware options



      Hello, Team~



      I'm laying out some Sanyo modules on paper. Twelve of them fit the roof 
with almost too much perfection: this would be difficult to install as it would 
fill the roof "edge to edge" in both directions. Are there consistent 
guidelines about the amount of roof edge which must remain uncluttered or is 
this mainly driven by the amount of aggravation that the installer is willing 
to tolerate? Which organizations would want to influence such decisions in the 
Atlanta region? Details are: residential, new construction, wooden truss type 
roof framing, finish roofing yet to be decided.



      I've seen fancy photos of rooftops which are covered edge to edge, but I 
suppose those are "building integrated" PV systems instead of discrete modules 
mounted above the roofing material. Who decides if those are "OK' for no 
walkways compared to a roof that is fully loaded with Sanyo type modules? How 
are such decisions made?



      I like the "top clamp" style mounts but UniRac SolarMount rail systems 
need about a 1" gap from one module to the next. Is there anyone with similar 
hardware that can get a grip within a smaller gap?



      Thanks in advance,


      Mick Abraham, Proprietor
      www.abrahamsolar.com

      Voice: 970-731-4675



      _______________________________________________
      List sponsored by Home Power magazine

      List Address: RE-wrenches@lists.re-wrenches.org

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org






    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org







------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to