Hi Marco:
    You are correct, I have noticed that most LBs do limit the fill area of 
your 
conduit.  As you probably notice, making a 90 bend requires some extra area, 
especially for large conductors.  This is one good reason to not fill the 
conduits to maximum capacity.  Most LBs and other boxes do list the area of the 
box on it.  If you are not sure, you should perform a calculation to determine 
how much of the total area you are consuming, based upon NEC requirements.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Marco Mangelsdorf <ma...@pvthawaii.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Thu, August 12, 2010 8:19:08 PM
Subject: [RE-wrenches] Aluminum conduit LBs

  
Anyone know where I could go to find out the max conductor sizes that threaded 
Al. LBs can handle?
 
I learned the hard way that a conduit of X inches that can handle conductors of 
a certain size does not necessarily mean that a LB of the same diameter can 
handle the same size conductors.
 
Thanks,
marco


      