Those HUP batteries are still under warranty and you very well may have a free
cell waiting for you, give Rob or Jean a call at NWES and run it past them.
They offer 1st rate CS and should take good care of you. You won't get much for
used batteries so I would be inclined to keep them in service even though 4
strings in parallel is not ideal. I've had reasonable luck with 4 strings
paralleled by getting my battery/inverter cables all over the bank, at the
least put 1/2 of your inverters across 2 strings and the other 1/2 on the
remaining 2 strings (still parallel all 4 strings).
You never mentioned an EQ cycle either, with that limited Absorption time it
should happen at least every 6 weeks.
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
>SOLutions