Nick:

Rhetorical questions to follow:

If you do not provide string calculations, how do you verify that Voc will not exceed NEC limits? How do you verify DC feeder ampacities? Does your jurisdiction not verify such parameters? We know you have a handle on these factors, but how about the Johnny-come-latelies trying to take your business? Should they not be kept to uniform standards meant to protect the safety of the consumer (and ensure fair competition)?

Can you really expect a field inspector or the customer to verify these parameters? I believe all of these issues are best handled by stringent plan check.

What is more important to you: saving a few bucks in permit fees or preventing house fires?

William Miller




At 05:01 PM 6/15/2010, you wrote:
Hi Jeff:
My standard permit docs are comprehensive, but do not include documentation regarding string sizing, thank goodness. A permit technician/ plan reviewer should not be overseeing string sizing. You should be thankful that the permit fees are so low, because that is the best thing a jurisdiction could do to support PV! Any fly-by-night, incompetent installer can check string sizing on the inverter manu's web site. I would suspect that, regardless of the plan review process, the less experienced installers will still be accountable to the inspector and their customer.

Nick Soleil
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to