Kirpal,
For the occasional odd high-current DC contactor, I like MDI. They made the mercury displacement contactors used years ago in the Ananda/APT Powercenters. Check out http://www.mdius.com/relays.php#High_Voltage to see if they have anything you can use.
Allan

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



Kirpal Khalsa wrote:
Hi All....thanks for the good feedback on this water pumping system.  Many good ideas....It looks like this is a system which can be done.  I will be looking for a relay that will have the necessary voltage characteristics which will have ~200VDC on one side being normally closed and 240VAC on the other side, normally open. 
Mark, Allan.....I am looking at the Grundfos SQFlex Battery Back up system brochure and it shows a SQFlex system running with a pressure tank in their example system.  Additionally they brochure goes on to say that "the CU 200 Controller has terminals for a pressure switch, which will control the pump's on/off  operation via the pressure in the storage tank.  The pressure switch  should be of a normally open configuration, where the contacts within the switch are in the open position when the pressure is below the maximum set-point.  When the pressure in the system rises to the maximum desired pressure, the contacts will close signaling the pump to shut off."  In researching further it looks like the float terminals in the CU 200 controller are able to be used for either a float switch or pressure switch.
I don't have any experience running a pressure tank in line with the output of the system but I can't see why as Allan pointed out that it would know the difference between 40PSI in a pressure tank or an additional 100' of head.  I think that it is important to recognize the additional head ( due to the pressure tank) that will be present and to take that into consideration when sizing the array for the desired amount of gpm production.
If anyone has any recommendations for a relay or other switch which can handle 200VDC and 240VAC I would be grateful.....
Cheers,
--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o

On Mon, May 24, 2010 at 2:42 PM, Mark Dickson <m...@oasismontana.com> wrote:

Allan,

This is all Dwight at Genpro could tell me. . .sorry to be vague!  I agree, it seems like it would not know the difference. 

 

I would love to shed some light, however this was shared with us at the NGWA show by a Grundfos Engineer.  It has brochursomething to do with the thrust load bearing on a them.  Lorentz has two I believe Grundfos has one.

 

Best regards,

 

Mark Dickson,

NABCEP Certified Solar PV Installer ™

Oasis Montana Inc.

 


From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Monday, May 24, 2010 2:39 PM


To: RE-wrenches
Subject: Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

 

Mark,
Your message gave me pause, as I just last week specified this setup, so I checked into it with our Grundfos rep. He said he had never heard anything recommending against the flex in a pressure system. He said the SQF doesn't know the difference between 40 psi and 100' of head. At the end of the day the pump just stops.

He did make a point of emphasizing the need for pressure relief valves, as the helical rotor models can overpressure a system.

Could you check with your distributor about this and post the reason you're given, please?
Allan

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



Mark Dickson wrote:

Our Grundfos pump distributor has always warned against using the SQF pumps in pressure pumping situations.  I can’t quite remember why, but you may want to check into that.  The Lorentz HR’s have been the choice in these situations.

 

Best regards,

 

Mark Dickson,

NABCEP Certified Solar PV Installer ™

Oasis Montana Inc.





_______________________________________________ List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to