Hi Rebekah,

The 48v is a max rating not a nominal rating.
So yes only good for 12 and 24v systems.

However with CBI breakers I don't understand why the need for QO for DC anymore?

jay

peltz power
On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:

> Hi,
> One thing to be clear about is whether these are listed for "48 volt 
> systems," or for max 48 volts?
> I was under the impression that they were max 48 volts, meaning you really 
> shouldn't use them on a system >24volts nominal.
> 
> Rebekah Hren
> North Carolina
>  
> 
> 
> http://thecarbonfreehome.com/
> 
> --- On Sat, 5/15/10, Kurt Albershardt <i...@es-ee.com> wrote:
> 
> From: Kurt Albershardt <i...@es-ee.com>
> Subject: Re: [RE-wrenches] AC breakers used in DC applications
> To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
> Date: Saturday, May 15, 2010, 12:59 AM
> 
> The Square-D catalogs are marginally clear on which breakers are listed for 
> DC and for what voltages, but when I tried to select an appropriate load 
> center for a DC application earlier this year I quickly ran into a number of 
> conflicts in their catalogs.  Here is the response from Schneider tech 
> support (Case# 4845778 on 1/19/10 in case anyone runs into problems with an 
> inspector):
> 
> 
> 
> The load center catalog numbers listed below are UL LISTED, File E6294, for 
> use on 48 V dc systems. The load centers listed ARE NOT MARKED for use on 
> this voltage system, however are suitable for the application. QO branch 
> breakers, 10-70 ampere (1 and 2 pole) are also UL LISTED for use on 48V dc 
> systems. Short circuit current rating is limited to 5,000 amperes when used 
> on 48V dc.
> QO24L70F, S or RB QO612L100F, S, DF, DS, DFCU, DSCU, RB, TRB or RBCU 
> QO816L100F, S, DF, DS, DFCU, DSCU, RB or RBCU
> QO112L125G or QO11224L125G QO116L125G QO11624L125G QO120L125G QO12024L125G 
> QO124L125G or QO12030L150G QO124L150G QO130L150G or QO112L200G or QO130L200G 
> or QO13040L200G QO142L225G or
> GRB or GRB
> or GRB
> GRB
> GRB GRB GRB or GRB QO142L225GRB
> 
> 
> I can email the PDF to anyone who needs a copy.
> 
>  

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to