Bob,
If I step back and look at your question, another bigger question comes up: if you are designing a system with two inverters in order to double charging current, you must have a pretty good sized battery bank. In general, I would suggest that you look at a 48V system, rather than 24V, once it gets to that size. Equivalent charging rate, but smaller wire, lower component amperage requirements and fewer battery strings to get the capacity you're apparently looking for.

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



Phil Undercuffler wrote:
If the normal connected loads are within the capacity of a single inverter (which may actually be possible -- I run my whole house off one Outback FX2024, microwave, dishwasher, washing machine and all) then you can just leave one of the inverters in sleep mode or disable output but leave input/charging enabled. 

Which inverters are you planning on using for the generator charging?  Depending upon which brand or how sophisticated you want to be, there are a couple ways to skin this cat.  Easiest and cheapest is to simply not connect up any AC output wiring or stacking cables to the second inverter, and program it to stay asleep and charge only when it sees AC input power.

I used to be religious about making sure my inverter was asleep, and even had a second baby inverter to power a handful of full time or sensitive loads.  However, it got difficult trying to explain why you couldn't just plug the vacuum cleaner into just-any-old-outlet, and as my electronic widget count expanded it became less and less advantageous to have that baby inverter.

Phil Undercuffler
Conergy





On Tue, May 11, 2010 at 9:58 AM, bob <reelli...@gmail.com> wrote:

I am sizing a system that will have dual inverters to shorten generator charging in the winter and enough solar to charge the rest of the time.

Here’s the problem, the inverter will not be able to get into sleep mode at night.

 

There are 2 cell chargers and a “cpap” machine having to run all night.

It only totals 26 watts, has anyone found a better way to do this without having to keep an inverter awake to produce 26 watts?

I would like to dedicate a Morningstar 300 watt inverter for the job but the system is 24 volts and Morningstar has no plans to make one in 24 volts.

 

Anyone got any other ideas, or am I best to just deal with it?

 

Thanks,

Bob


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________ List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to