Hi Jeff,

I probably should mentioned that many of our float switch wire runs exceed 3,000 feet from tank to Cu200. We use shielded, direct burial rated 18/2 cable, bury the wire and ground the drain wire at the controller.

So with those "long distance" systems, do you think a relay would work? It just doesn't seem feasible to run coil voltage that far. That's why we've been relying on the CU-200 microprocessor to do the job. Also, I
don't like to run anything but the pump off a PV direct system.

As for the pressure tank/ switch option, we do have a few of those out there and I agree, they work fine. But on some of our systems the vertical rise between the pump and storage tank is over 300 feet. That's about 130 psi and those pressure tanks wouldn't like that too much. And for various design reasons, a check valve on the main feed line isn't feasible, so we ruled out the pressure switch option on these "long distance"
systems.

I also like to keep things as simple as possible where livestock water is concerned. Farmers have so many maintenance items on their list now, I hate to add more. So at first look, the Cu200 seemed to be the ticket.

Thanks for the info!

Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV&  wind installer
PA Sunshine Program Approved PV Installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747

www.four-winds-energy.com

Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.

===============================================
The 6th Annual Small Wind Conference
A Gathering of small wind industry stakeholders
June 15 and 16, 2010
Stevens Point, Wisconsin
i...@smallwindconference.com
http://www.smallwindconference.com


On 4/22/2010 4:20 PM, Jeff Oldham wrote:
Hi Roy,

You do have a choice about controllers, as I mentioned I use off-the-shelf 
components. For your need you have at least 2 sweet options - 1) get a relay to 
switch the pump power and use a float switch to control the coil, go with a SSR 
for even higher reliability.  This is a $50 substitute for a $300 CU-200. 2) 
Use a Cla-val at the tank and a pressure switch and 2gal press. tank at the 
pump. This works at any distance w/o control wires and is fully hydraulic and 
highly reliable plus this valve does not throttle as it reaches full. This is 
my control of choice if the distance between pump and tank is much over 400', 
cost must be considered as this is about a $700 setup.

-jeff o

> From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative 
SOLutions

____________________________________________________________
Penny Stock Jumping 2000%
Sign up to the #1 voted penny stock newsletter for free today!
http://thirdpartyoffers.juno.com/TGL3131/4bd0afe9e1274a5860st03vuc
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to