Jim,

 

You have probably seen this already but it’s worth a mention here. Good article 
in SolarPro magazine April/May “Optimal PV-to-Inverter Sizing Ratio”.  

 

Dave

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 7:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

 

Im sorry, I meant to write “11 modules per string” below.. 

Been a long day..

 

From: Jim MacDonald 
Sent: Monday, April 19, 2010 7:41 PM
To: RE-wrenches
Cc: Jason Szrom
Subject: RE: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

 

SB8000US only good for 480 Vac, we’re tying in at 208.

 

11 strings [11 modules per string] has been calc’d to be OK (<600vdc) for 
record low -4 fahrenheit (-20 celsius).

 

I think the big concern as mentioned is getting the Voc high early in the AM to 
wake the inverter up, also maintaining the Vmp later in the day to keep it 
running for as long as possible into the late afternoon/ evening.

Will those extra kWh gleaned in the early AM/ late PM over the course of 365 
days be more than the kWh clipped during peak production times with the 9.075 
kWdc?

NYC average summer highs between 79 and 84 fahrenheit early june-late august.  
Sunlink rack @ 10° on a silver-painted built-up roof.

 

Time-of-use utility $ peak-shaving is not an issue here.

 

Thank you

 

 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to