Brian Teitelbaum wrote:
Hi boB,

The issue is whether the generator is rated for use as "prime power" or rated as 
"back-up power". Prime power units will get considerably more run-time hours on them then 
generators used in back-up. At least that is what the generator manufacturers think.

Once upon a time it didn't matter. The engines were heavy cast iron, and 
running at slow speeds, usually 1800RPM, but sometimes as low as 1200RPM, and 
lasted for thousands of hours of run time. As the manufacturers switched to 
cheaper aluminum engines running at 3600, the amount of hours before a major 
rebuild was required decreased. Honda, and others, were able to bring aluminum 
engines back up to fairly long life-spans, but they are still not as rugged as 
those old hunks of iron. Emission regulations further destroyed the old iron 
engines, unless you get one big enough to have 4-cylinders.

There is no reason, other than cost, for Kohler to not make a 4-cylinder, cast 
iron, 1800RPM, prime-power unit, but maybe they feel that there just isn't 
enough of a market for them to build it. I think that they are wrong, but I 
don't know the true numbers.

The real problem is that the generator manufacturers don't understand how 
off-grid systems work these days. 20 years ago, you could expect an off-grid 
generator to rack up considerable hours in a short time. These days, we get PV 
to do that, and the genny is just used for back-up. If the system is designed 
properly, the genny should get minimal hours per year, and the manufacturer 
should be able to warranty them. They need to be educated.

Brian Teitelbaum
AEE Solar



Thanks Brian. Yes, I do believe they need to be educated that these days, their generators, even backup rather than prim power classes, are more of a backup. If they wanted to, they could just use the run time meter to decide if it is warranty or not, maybe.

Thanks again,
boB











-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Tuesday, March 30, 2010 12:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Kohler Generator Issues

Nick Soleil wrote:
Hi Jeff:
I have had some similar issues with the Kohler generators in recent years, after installing hundreds of air cooled and water cooled generators from them. I have heard that they are less reliable now, and the company is harder to deal with now. Recently, I tried a Generac in an off-grid project, which I have found is even more difficult to work with. They don't warranty the product for off-grid applications, it requires hard wiring a battery charger, and it starts and stops based on utility sensing, which required installation of a relay to switch the sensing circuit on and off. It was a pain to deal with, and required a few more trips to the site than I would have liked. On a similar note, Xantrex provided the Auto Gen Start module, but it did not support 2-wire start! Isn't that the most common gen start configuration? The newer versions do offer that now.


Is this "no warranty if used off grid" in writing from these manufacturers, or is it just some salespeople saying this ?

Why would you need a generator if you have grid available ?

boB




Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037


------------------------------------------------------------------------
*From:* Jeff Yago <jry...@netscape.com>
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Sent:* Mon, March 29, 2010 7:53:18 AM
*Subject:* Re: [RE-wrenches] Kohler Generator Issues


Although we have specified and included Kohler RES models in all our off-grid and battery based solar projects for over 15 years, we have seen a real decline in the suitability of the Kohler line in the past few years for use in solar/battery/generator applications. First they killed off the 1800 RPM units under 15 kW. We had many older systems that would not work when we replaced an aging 1800 RPM unit with their same kW size new 3600 RPM units, which made inverters go nuts with under-voltage and over-current errors.

Then several years ago they got rid of the battery charging alternator or whatever that re-charged the battery when the generator was running as a way to reduce costs, so now the only way to keep the battery charged was to plug in a full time float charger. This 24/7 electrical load is not a good idea for smaller off-grid systems and requires another set of wires out to the generator to supply this outlet. Finally, Kohler added a diagnostic electronics panel that adds another 24/7 electrical load. We "kill" this off during installation on any off-grid application as we cannot justify this 24/7 standby load. There is a software switch to do this, but its not easy to find in the instructions.

Funny thing was the other day I received a call from the main Kohler factory about some marketing issues and I finally let loose with the above rant. I really complained that so far they have done everything they could NOT to serve this very large and growing off-grid market, and I pointed out that most of their recent design "improvements" made their generators LESS suitable for this market, not better. This guy was absolutely dumb-struck, and it appears to me that they have made no effort to understand this market. Their more recent efforts to void warranties is just another reason to look for a different generator supplier.

Has anyone on this list had any contact from Kohler central office about finding out what features this industry needs? The guy I talked with may be just blowing smoke, but he promised to have a followup call in next few weeks to learn more about what they can do. According to him, he thinks they can add a software "switch" in the programming for little or no cost like "on/grid - off/grid" that we could access during setup that would adjust generator parameters and standby losses when used in an inverter-battery application. In case he really does followup, are there any other rants I could include from you guys that have been a problem for you when using Kohler generators. I will assume we are limiting this to their non-water cooled units under 15 kW.

While ranting on generators, the main reason we liked to use Kohler was the easy 2-wire start/stop connections you can connect to the aux relay in most inverters, while many other generator brands were not easy to remote start from an inverter or required multi-step starting relays. Has this changed, and are there now other brands of generators in the 8 to 15 kW range that work well for backup of solar/battery charging applications and the manufacturer does not have warranty issues when used in off-grid applications?

Thanks,

Jeff Yago

_____________________________________________________________
Netscape.  Just the Net You Need.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to