Hello Darryl,

I look forward to learning how you match solar production time with 
consumption. I'm sure other wrenches do too.

Los Angeles has generally sunny weather with May and June coastal fog and 
unpredictable clouds and rain from November until April. It hardly rains from 
July through  November so PV users can occasionally benefit from demand offset 
from PV.

Here is a manual method for managing demand that others may find useful. A 
cabinet making shop owner with a grid-tied PV system is able to control his 
demand rate manually. Before he installed PV, he put a red light in the shop to 
warn workers when demand was greater than his desired amount so workers could 
manually shut off loads within the 15 minute demand period. PV has allowed him 
to lower his demand goal, but they still has to keep an eye on the red warning 
light.

Joel Davidson 
  ----- Original Message ----- 
  From: Darryl Thayer 
  To: RE-wrenches 
  Sent: Friday, March 19, 2010 6:24 PM
  Subject: Re: [RE-wrenches] Demand Charge Reduction by PV


        I do not agree. However I can not disagree with such logic.  I hve done 
some demand reduction, and I am doing some more.  I did not say it was easy.  
In fact it is hard, it is expensive, and in my area the energy saving for solar 
for anyone on the general service rate (demand billing) is a fool to invest on 
a ROI basis.  HOwever if the demand can be reduced in my area it is more 
valuable than the saving from energy reduction.  My present customer has a load 
factor of 10% I am studing this load profile on a fifteen minute recorder.  I 
hope to in about 2 weeks have enough data to make my predition as to energy 
saving from the solar with demand reduction   
        As a note, I do not need to see the future, but the use structure has 
to be known, so as matt says the unlikley day does not show up and ruenin the 
month.  Indeed not all buildings can be demand reduced.   It is possible the 
"electricity use profiles" in your location is different from Minnesota, .
        Darryl
        --- On Fri, 3/19/10, Matt Lafferty <gilliga...@gmail.com> wrote:


          From: Matt Lafferty <gilliga...@gmail.com>
          Subject: Re: [RE-wrenches] Demand Charge Reduction by PV
          To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
          Date: Friday, March 19, 2010, 2:26 PM


          Wrenches,

          I agree with Joel.

          This is my policy on the matter: Consider any Demand Charge 
reductions to be bonuses in favor of the customer. I think it is OK to say that 
there MAY be some savings, but DO NOT try to guarantee or insinuate that there 
WILL be any Demand related savings. 

          Here's why: UNLESS you have multi-year interval data for the site... 
AND the ability to accurately interpret it.... AND the facility has a favorable 
tariff... AND a site with a very predictable load (think in terms of being able 
to predict the 15-minute interval which will set the Demand Charge within +/- 1 
hour)... AND the 15-minute period which would otherwise set the Demand Charge 
coincides with a period when the PV system is operating at a predictable 
output.... AND your overlay of predicted generation on top of predicted load 
indicates a FANTASTIC Demand reduction... AND your proposed system has multiple 
inverters (the more the merrier here)... AND the weather is reliably 
predictable around the 1-hour period you predict the "new" Peak Demand to 
occur... Don't bother having the conversation or spending otherwise productive 
time analyzing the matter... 

          If all the the ANDs above are true and you really want to go thru the 
exercise, for whatever reasons you may have, be sure to consider the following: 
In order to "prove" whether or not there was an effect on the Demand Charges 
due to the PV system after the fact, you will need to have interval data for 
both the generation and the facility. You will need to be able to evaluate 
whether or not the customer's load profile, independent of the PV, changed from 
the predicted values and, if it did, what the reasons for that were. For 
example, if they increase or decrease their loads independent of the PV, the 
net change is due to the customer's actions and the PV. Once you have 
determined these factors, then you can begin to calculate the effective "value" 
of the PV was on a Demand Charge basis.

          It is possible and, in fact, likely that the PV will have some 
positive effect on the Demand Charges for a given facility. It is, however, 
very difficult to predict what that will be unless all of the ANDs noted above 
are true. One of the keys driving the final calculation is the ratio of the PV 
system's power rating to the customer's load coincident to the 15-minute 
interval when the Demand Charges are set. The larger the system is, compared to 
the facility load, the more likely and greater the savings will be. Embedded in 
this relationship are the seasonal and hourly load profiles of the facility, 
the reliability of the weather during this period, and how closely they line up 
with the production profile. If you are intending to "guarantee" some number of 
kW reduction, be sure you have multiple inverters on the project. The more 
inverters you have, the more confidence you can have in your predictions. 

          Over the years, I've spent plenty of brain-damaging hours (weeks & 
weeks) working on this. For utility companies, large integrators, and small 
integrators. Before and after installation. With and without complex load and 
generation profile data. On facilities with loads of all magnitudes and 
hourly/seasonal profiles. The end result is the same... The effective Demand 
Charge savings due strictly to the PV is relatively small and terribly 
difficult to predict from year to year. I've had to analyze and report on "why" 
the mucky-muck MBA & Engineers' predictions were so far off from the actual 
experience after the projects went in. In the minds of these folks, it seems 
like a no-brainer and just another column in their spreadsheets during the 
sales cycle. It's a lot more complicated than that. I know of several 
institutional customers who bought into paying the integrator for these Demand 
savings on projects and have walked away from doing it on future projects. The 
ones who have bought into paying for projected future Demand reductions in the 
up-front cost of the project have regretted it. The ones who have agreed to pay 
for it as a line-item on a PPA bill, aren't doing it in the future. It's simply 
too much brain-damage. Too complex. If they are going to have to pay somebody 
for it, it's a lot easier to pay the utility company.

          I've had to analyze and report on cases where the facility Demand 
Charges have increased after installation of PV systems. After you isolate the 
load and generation factors, and demonstrate that the customer's load profile 
has changed from the historical (generally larger loads later in the day when 
the PV can't help as much), you can do the dance of trying to show them that 
they avoided something and trying to quantify exactly what that is/was. A lot 
of Demand tariffs actually punish lower kWh consumption, so you have to factor 
that negative impact into the value analysis. A LOT of time goes into this when 
you consider all the communication, data gathering, analyisis, presentation, 
and negotiation. Remember, it only takes one 15-minute period that occurs 
outside of your effective generation curve to blow the whole theoretical thing 
up.

          IF you are set on going thru the exercise with the intent of 
predicting/promising something, you need a facility with a very stable load 
profile that occurs during peak PV periods, stable utility voltage, a tariff 
that doesn't punish lower consumption, reliably predictable & favorable weather 
coincident with facility peak demand, a large PV to Load ratio (>50%), and 
multiple inverters. The combination of requisite weather, PV:Load ratio, and 
favorable tariff pretty much makes the number of facilites, which you can model 
accurately, very small.

          I recommend going to the beach or mountains instead.

          $0.02001
          Solar Janitor



----------------------------------------------------------------------
          From: Joel Davidson
          Sent: Thursday, March 18, 2010 7:47 PM
          To: RE-wrenches
          Subject: Re: [RE-wrenches] Demand Charge Reduction by PV


          Hello Peter,

          I have seen 40% to 70% monthly demand charge reduction for some 
southern California PV projects for some months, but it is still a crap shoot. 
15 minutes and 1 second of clouds during the peak demand period will trump a 
client's energy management efforts unless they are willing and able to shed 
loads during cloudy periods. I tell clients that they cannot rely on the 
weather to cooperate, to monitor and control their demand, and to think of any 
PV savings on their monthly demand charge as a windfall.

          Joel Davidson

          ----- Original Message ----- 
            From: Peter Parrish 
            To: 'RE-wrenches' 
            Sent: Thursday, March 18, 2010 9:38 AM
            Subject: [RE-wrenches] Demand Charge Reduction by PV


            I failed to clean up the subject line on this post a few minutes 
ago. Please respond to this post so that we can keep track of the topic 
properly.



          Esteemed wrenches,



          I have been wrestling with this concept about as long as we have been 
in business. How to estimate how much a pv system will reduce the demand charge 
for a customer.



          I know the “worst case” goes as follows: 



          (1)     Demand is based on measuring the consumption every 15 minutes 
and keeping track of those numbers for the entire billing period.

          (2)     The customer gets socked with a demand charge that is based 
on the highest 15 minute consumption for the entire billing period.

          (3)     The customer also gets soaked with a “facilities charge” that 
is equal to the greatest monthly demand number for the trailing 12 months.

          (4)     Now you have a solar system pumping out Wac varying over the 
familiar bell-shaped curve during the day.

          (5)     In the southwest US, peak demand typically occurs early in 
the afternoon in the summer, during the week. Our LADWP has a mantra that goes 
something like this, “Peak demand occurs at 3pm PDT on the third Thursday in 
August!” I believe them.

          (6)     So one would expect something like 40% of the peak Wac to 
offset the peak demand, but what happened if the sun goes behind a cloud for 
those 15 minutes? Answer, “Bad luck. Your demand is back to what it was before 
you bought your solar system.

          (7)     It is actually worse than that. Peak demand recurs with 
approximately with the same value with some regularity for an extended period 
of time, so the sun will have to shine with full intensity every day when peak 
demand is expected to occur, which in LA could be every day (M-F) of the 30 day 
billing period.



          I have always taken the position that we can’t guarantee that any of 
the demand charge will be reduced with a solar system. But what do other PV 
integrators tell there customers? Better yet is there any actual data on demand 
reduction with PV systems? It seems to me that occasionally the monthly peak 
demand will in fact be shaved by PV production, the question is how often in 
practice?



          I once thought of taking actual insolation data and comparing it with 
actual demand data and doing a Monte Carlo simulation (throwing the dice = 
randomly matching up demand data with solar production data) – but I haven’t 
retired yet.



          I would love to hear what others are doing about this.



          - Peter

          Peter T. Parrish, Ph.D., President
          California Solar Engineering, Inc.
          820 Cynthia Ave. , Los Angeles , CA 90065
          CA Lic. 854779, NABCEP Cert. 031806-26
          peter.parr...@calsolareng.com  
          Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885                
                                                                                
   

        -----Inline Attachment Follows-----


        _______________________________________________
        List sponsored by Home Power magazine

        List Address: RE-wrenches@lists.re-wrenches.org

        Options & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm

        Check out participant bios:
        www.members.re-wrenches.org

       




------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to