Colleagues:

I have a good friend that is a licensed electrical engineer. I forwarded to him the background about the Yorba Linda certification requirement. Below is his response, which I think is very pertinent to this list. I redacted his name and contact information because I forgot to ask his permission to post his response to the list. If anyone wishes to pose any questions, I can forward.

With any PV system in the field, there are several variables which are difficult to quantify: Insolation, both instantaneous and over time, temperature at the module, and wind speed. When I am looking at a PV system to evaluate suitable operation, there is some subjectivity in determining acceptable output. I believe it would be difficult to give a go or no-go determination to a given system. As my friend asks below, "who sets the standards, and what are they?"

William Miller




Generally problems in this area come down to legal definitions. You used the word "commission", they use the words "test and approve". Some of these words have legal meanings that assign risk and liability. This is a common misconception. Engineers design systems and set the parameters that constitute the performance metrics of that system. Like the men and women at Siemens or Square D. Once these metrics are established, they can be used by qualified installers and technicians as benchmarks in the field to determine if the system is performing as designed. So first off, you do not need an engineer to perform tests: The performance parameters are published, the inspector witnesses a field test by the installing contractor or testing agency technician that demonstrates the parameters are met and you're done. Second, most engineers have little or no actual experience field testing electrical equipment. Many wouldn't even know what a megger is or how to use it. A trained technician is typically far better trained and equipped to perform this task. There are good size companies such as ElectroTest that do this stuff exclusively and there isn't an engineer in the bunch (except in their offices). Finally, the main reason to use a registered engineer is to protect the public concerning life safety issues and so you can assign professional liability. That is why the state requires the license and insurance. My professional liability policy specifically limits any testing and "approval" activities I perform. They typically will not cover any of it. Only systems I design and even then there is a limit of liability concerning the manufactured equipment (tested and listed by others) used within the system. Which is why I said a registered engineer would be foolish to do this. So if the City thinks they are getting something (such as professional responsibility) by requiring this, they are misinformed and I am serious when I recommend they call the state board and ask them about this requirement. I am sure the board will dissuade them from this. As far as a business model, I would think a specialty contractor would be the best for this. But really it begs the question: What is it they are thinking you are going to test? Voltage? Output? Grounding safety? Who is publishing testing guidelines that someone can use to constitute an "approved" installation? It is just half baked bureaucratic psychobabble and should be challenged as such. That is my two cents. J


G__:

I am curious about you response. What problems do you see with a registered engineer commissioning a grid-tie system. The consensus is that there is little to test with one of these systems. A voltmeter, ammeter, insolation meter and maybe a megger are all that are required.

William



At 03:14 PM 12/21/2009, you wrote:

Incredible. What "registered engineer" would be foolish enough to "test and approve" something like this? I would recommend the city of Yorba Linda call the state board and ask them what they think of this statement. It is patently misguided.

G___ N___


From: William Miller [<mailto:will...@millersolar.com>mailto:will...@millersolar.com]
Sent: Friday, December 18, 2009 3:09 PM
To: g___
Subject: Fwd: [RE-wrenches] Solar System Certification

G___:

The posting below is from an industry chat list. I though you might find it interesting.

The ordinance can be found at: <http://www.municode.com/resources/gateway.asp?pid=13406&sid=5>http://www.municode.com/resources/gateway.asp?pid=13406&sid=5 This requirement is not a bad idea. It would drive up the cost of PV, but it would protect consumers. Would be a good line of work for someone with your credentials.

William




I am curious if any of you have had to deal with this issue before.

The following is an item we got back from the City of Yorba Linda for a Plan Check correction:


All electrical solar systems shall be tested and approved by a California Registered Electrical Engineer. The engineer shall furnish a report stating their name, registration number, its date of expiration, address where the testing occurred and the dates of testing and approval. Such report shall be presented to the City inspector for approval at the time of final inspection. (YLMC 15.28.020) Note on the plans.

All experiences and suggestion are appreciated.



Best Regards,
Brian C. White
Design Engineer - PV Systems

Eagle Roofing Products
120 North Auburn Street - Suite 212
Grass Valley, CA  95945
Phone: 530-273-2948
Cell: 530-575-5550
e-mail: bri...@eagleroofing.com <<mailto:bri...@eagleroofing.com>mailto:bri...@eagleroofing.com>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to