We have seen one failure mode with sealed batteries that stands out, and that 
is long term overcharging. Two reasons for that, one is from failing to set the 
correct charging voltage, but another main one is not using temperature 
compensation. The charging voltage for batteries should go down quite a bit at 
higher temperatures - but without temp comp that won't happen. If you boil 
flooded batteries you can add water, with sealed batteries not so easy.

..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
  ----- Original Message ----- 
  From: Dana 
  To: 'RE-wrenches' 
  Sent: Tuesday, December 01, 2009 7:35 AM
  Subject: [RE-wrenches] sealed revival


  Travis - I echo your results on the addition [per manufacturer's directions] 
of distilled water and application of a deep re-charge [eq.] charge, I got 4 to 
6 months on the 3 banks that we attempted to revive. If we think wet lead acid 
batteries are a fragile chemical equation then sealed batteries are even more 
fragile.

   

  Dana Orzel

   

  Great Solar Works, Inc

  www.solarwork.com

  E - d...@solarwork.com

  V - 970.626.5253

  F - 970.626.4140

  C - 970.209.4076

   

  I will be the shift in how the world uses power! - Dana Orzel
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to