wow wrenches,

fun solar day for me. Another supply side tap nightmare.

Have any of you ran into a situation where the AHJ will not let you upgrade the 
feeders from the meter to the
 main breaker because it "voids the UL listing"? In this case I had 1 AWG 
feeding a 100 amp main, but it was
 type TW which is not on the feeder exception 310.16. In running into the 
typical daftness on 690.64 I asked
 if I could replace the 1 AWG TW with Type THHN so the feeder chart would apply 
and there would be 150
 ampacity wires feeding the 100 amp main. No luck, all frustration.

Any wrenches have any thoughts on this?

Nick Vida



      