wow wrenches, fun solar day for me. Another supply side tap nightmare.
Have any of you ran into a situation where the AHJ will not let you upgrade the feeders from the meter to the main breaker because it "voids the UL listing"? In this case I had 1 AWG feeding a 100 amp main, but it was type TW which is not on the feeder exception 310.16. In running into the typical daftness on 690.64 I asked if I could replace the 1 AWG TW with Type THHN so the feeder chart would apply and there would be 150 ampacity wires feeding the 100 amp main. No luck, all frustration. Any wrenches have any thoughts on this? Nick Vida
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org