Kent,

Thanks for helping sort out this issue. At a minimum, the majority of the portable generators being connected to wiring systems today are not code compliant. Fortunately, the connections haven't created incidents, since these systems have become very common. Off grid installations must be in the minority.

Over the past several years, many major storms have left millions of people without power. Small generator sales have skyrocketed. Utility companies pleaded with people not to backfeed breakers, but to use a transfer switch. Now, as it turns out, the 4 wire connections to wiring systems via transfer switches, provided by commercially available generator inlet boxes, create a code violation do to parallel neutral paths.

Maybe portable generators should be arranged like mobile generators, where available lugs make bonding the neutral to frame (or not) very simple. Hooking up a 220 KVA mobile generator, for a concert, was really easy.

If the chasis could be un-bonded easily, permanent rod could be installed, that the portable generator could hook to when moved to its backup power location. Or, maybe the NEC should be amended to allow people who have lost power in emergency situations, to connect to a portable generator. Maybe even extend this to solar backup systems, if no real world hazards can be demonstrated.

I'm still not convinced that it is not legal to hook into a grounded and bonded wiring system, so long as the equipment grounding conductor is omitted. Here is the code section on portable generators:
____________________________________________________________________________________________
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions: (1) The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and (2) The normally non–current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
____________________________________________________________________________________________________

Nothing here says we can't connect to a wiring system via cord and plug. If we omit the EGC, which runs in parallel with the neutral, parallel neutral paths don't exist. Maybe it is inferred somewhere else, or enforced by interpretation. RV and marine inverters do switch the neutrals, creating separately derived systems.

Up until lately, it was permitted to ground the frames of electric ranges and clothes dryers with a neutral wire. Although this is not permitted for new systems anymore, I don't know of any incidents that have occurred. If there is no hazard involved, maybe the NEC could accept 3 wire connections for 120/240 V portable generators.

It would be good to find a solution to this issue that does not require hundreds of dollars of additional equipment and installation time, especially if no real dangers exist. If hazards to exist, equipment needs to be developed to address them.

Drake





At 01:06 PM 11/12/2009, you wrote:
Drake, I agree with you that there may not be a code compliant way to connect a portable generator other than to use a transfer switch that also switches the neutral. And non-the-less many portable generators are being used for backup power without a switched neutral -- without incident.

The older codes only allowed using the neutral to be grounded at separate structures if there was no other metallic path between the buildings. It was safe, still would be safe and I think it is a mistake for the code to be changed to disallow it. But the "no other metallic path between the buildings" requirement was often ignored. It is pretty rare to see metallic water pipes these days; but phone lines (soon to be history too), gas lines, intercoms, and so on are often added after word. And when they are grounded at both buildings, they carry a share (a small portion) of the neutral current.

NEC 250.34(A) says a grounding electrode isn't required if 1) the portable generator supplies loads connected by plug and cord and 2) non-current carrying metallic parts and equipment grounding terminals of the receptacles are connected to the generator frame. Sorry, Drake, the intent here is that an EGC is used. Using the neutral to connect the equipment grounds doesn't comply.

NEC 250.34(B) says the same thing for vehicle mounted generators that are bonded to the vehicle.

NEC 250.34(C) requires the generator neutral to be bonded to the generator frame if the generator is a separately derived system. If the generator can be used as a portable power source, it will be a standalone separately derived system and the neutral and ground must be bonded. Despite advise seen on this list serve, the neutral ground connection on a portable generator should not be disconnected.

There is a FPN in 250.34(C) refering to 250.20(D) for grounding portable generators supplying fixed wiring systems. NEC 250.20(D) covers system grounding for separately derived systems, that is when the generator neutral isn't solidly connected to the service-supplied neutral and the load neutral is switched between the two systems. This is the code compliant method to connect a portable generator to a fixed wiring system. Unfortunately the inverters we use aren't set up to switch the neutral; they aren't really set up to connect to a portable generator at all. And yet many portable generators are being connected to inverter systems and also directly to buildings for backup power -- without incident.

The FPN in 250.20(D) talks about on-site generators that are not separately derived systems and defines them as having a grounded conductor that is solidly interconnected to the service supplied grounded conductor (then the generator neutral ground bond is omitted). Most inverters are set up for this type of generator connection: a fixed on-site generator than can have a solid neutral bond between the different power sources. Yet, often, the customer wants to use portable generator. Hence our catch 22.

I like Alan's work around using the autotransformer as a generator balancer thereby forcing the neutral current to zero. It is an expensive piece to add to a small generator. But the Outback x-240 is only large enough to use for a small generator.

Kent Osterberg
Blue Mountain Solar


Drake Chamberlin wrote:
There may be no totally compliant way of using the internally-bonded-neutral generators, but they are being used a lot in both solar applications and emergency generator backup systems. Inlet receptacles and transfer switches are being sold in quantity for use with cord and plug connected generators, most of which are internally bonded.

Using a 3 to 2 prong adaptor might be the best solution where code rigidity is not the norm. In the old code, the neutral could be separately bonded at different structures under the same management. Using the adaptor, the neutral bonds to the frame of the generator, so other receptacles on it will still be legitimate to use in accordance with 250.34

The building will get its ground through the grounding electrode system of the building. There are no parallel neutral paths. All will have normal safety feathers and will function well. It may or may not be "code." Check out 250.34. I think there is some argument for this method being compliant.

Drake


Content-Language: en-us

The problem of the bonded chassis in most generators has been with us for years, and there is no real solution. With most cheap (and ubiquitous) portables, the AC neutral is internally bonded to the chassis and can’t be easily undone. When I wrote the HP generator article I attempted to address this issue without getting too technical. I ran this specific issue by John Wiles for his advice, and the final wording reflected his position that the AC ground loop – that is, maintaining the neutral-ground bond in both the generator and the inverter system and accepting that the ground conductor would carry a portion of any current otherwise being carried on the neutral – was the best of the options.

· The final wording as submitted to HP was: “Quality generators allow the neutral conductor to either connect to the generator chassis (for prime power application) or remain separate from it. Portable generators are seldom properly grounded, so manufacturers ground the neutral output conductor to the chassis. When connected into a grounded power system, however, this presents a safety hazard, as the neutral is now bonded to the ground at two places­one in the power system AC and one in the generator­and the safety ground wire becomes current-carrying. Some units also include AC ground-fault protection, which is incompatible with connection to a grounded power system. There is no simple, Code-compliant solution to this. The safest noncompliant approach is to bundle an insulated green ground conductor with the power conductors between the generator and the main ground buss, to both ground the chassis and minimize shock potential.”

Inherent in this is that that grounding conductor between gennie and ground buss be bundled in conduit and boxes, rather than being left bare or exposed, as would otherwise be OK with any grounding conductor.


Allan Sindelar
<mailto:al...@positiveenergysolar.com>al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
<http://www.positiveenergysolar.com/>www.PositiveEnergySolar.com

Larry,
Sounds like there are two neutral ground bonds: one at the generator and one at the house. This causes part of the neutral current to flow on the ground - a guaranteed way to trip the GFI. This is the catch 22 of connecting a portable generator, or one with an outlet, to a house system. The house panel has to have a neutral ground bond. The generator also has to have a neutral ground bond (Although the small Honda and Yamaha inverter generators don't. How do they get away with that? - No exposed metal to touch I guess.) or the GFI won't work and ground faults won't trip the generator output breakers.

Solutions (unfortunately none of these may be suitable and they all have potential problems):

Permanently wire the generator. On the generator, remove the neutral/ground bond and remove all of the electric outlets. In some locations, you aren't allowed to permanently wire a generator unless it is U/L listed. And most (maybe all) portable generators aren't U/L listed.

Replace the GFI outlet with a non-GFI outlet (so it will be like the old Homelight generator). Part of the neutral current will flow on the ground wire. That's a code violation, but for 20 and 30-amp outlets the ground wire has adequate ampacity so nothing is going to overheat. In fact, even 6 AWG SO cord has a ground wire the same size as the conductors.

Use a 2-prong cheater. This will prevent the GFI from tripping. It also prevents any ground fault past the cheater from returning to the generator. It's probably best to locate the cheater at the load end of the cord; that way if the cord is damaged the GFI will still trip. If there is ground fault past the cheater, there will be one or probably more than one locations where there is shock hazard. If you touch the generator frame, it'll tingle; if the ground is wet, it might be severe.

Use a mobile-style inverter that will switch the neutral/ground bond. Most of these are not U/L for house wiring. I think this is the best solution but it doesn't cover the circumstance of a grid backup inverter connected to a portable generator.

See. I don't have any good solutions.

Kent Osterberg
Blue Mountain Solar
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to