Drake,
Is the Eco Throttle turned off? If it's on, the generator is waiting
for a load to come up to voltage, and the inverter is waiting for
voltage to connect...
Good luck,
Randy Brooks
Brooks Solar, Inc.
Solar Power for People
140 Columbia View
Chelan, WA 98816
509-682-9646
ra...@brookssolar.com
www.BrooksSolar.com
On Oct 29, 2009, at 4:25 PM, drake.chamber...@redwoodalliance.org wrote:
Hello Wrenches,
I was under the impression that he Honda EU series of inverter
generators
could synchronize with the grid tie VFX inverters. I tried to do this
today with a 2000 EU, and the inverter would not accept the power. The
generator has low hours on it.
Does anyone know why the two won't sync? Are others having success
with
this combination? Has anyone else had this problem? Does the
generator
have any settings?
Thank you,
Drake
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org