I just had a conversation with a plan checker in LA County yesterday on that 
very topic.
 
When I directed him to NEC 690.14(C)(1) & 690.31(E):
 
690.14(C)(1) Location.
The photovoltaic disconnecting means shall be installed at a readily accessible 
location either on the outside of a building or structure or inside nearest the 
point of entrance of the system conductors.
Exception: Installations that comply with 690.31(E) shall be permitted to have 
the disconnecting means located remote from the point of entry of the system 
conductors.
 
690.31(E) Direct-Current Photovoltaic Source and Output Circuits Inside a 
Building.
Where direct current photovoltaic source or output circuits of a 
utility-interactive inverter from a building integrated or other photovoltaic 
system are run inside a building or structure, they shall be contained in 
metallic raceways or enclosures from the point of penetration of the surface of 
the building or structure to the first readily accessible disconnecting means. 
The disconnecting means shall comply with 690.14(A )through 690.14(D).
 
After we discussed these articles and the appropriate labeling of the metallic 
conduit, he waived the requirement.
 
Brian C. White
Sr. Design Engineer - PV Systems
 
Eagle Roofing Products
120 North Auburn Street - Suite 212
Grass Valley, CA  95945
Phone: 530-273-2948
Cell: 530-575-5550
e-mail: [email protected] <mailto:[email protected]> 
 
 

________________________________

From: [email protected] on behalf of Nick Vida
Sent: Tue 9/22/2009 6:38 PM
To: wrenches
Subject: [RE-wrenches] Rooftop DC disconnects


this is already required in Los Angeles county in a county ordinance. They are 
looking for dc disconnect directly after any combiner box and no conduit 
entering a building without disconnect- both commercial and residential. You 
wont see it in NEC unless you look in the 2002. I dont have the ordinance 
handy, but the plan check in those offices have the reference.


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to