Colleagues:

There is no shame in referring to these devices as reducers. As long as the smallest conductor size meets ampacity and voltage drop ratings, the use of larger copper is something to be proud of. It indicates an awareness of efficiency through design.

We don't favor splices that are not secured to a mounting surface. We want to be able to access a conductor for testing and labelling and we want to know where it is in a given enclosure. Therefore we use power distribution blocks such as those manufactured by Greaves, Ilsco and Square D. Here is a link to Illsco: http://tinyurl.com/l6msc6

This links shows these in the field: http://millersolar.com/Portfolio/Inverters/battery_iinverters/GH_FX/GH_Outback.html

William Miller





At 07:17 PM 9/21/2009, you wrote:


Hi Karpal,

Insulated Cable Terminal Blocks, like the ones made by Polaris and others, work really well.

Polaris: <http://www.polarisconnectors.com/fine_stranded_grey.html>http://www.polarisconnectors.com/fine_stranded_grey.html

Or Ilsco: <http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d>http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d

Or, you can also use a splicer right at the inverter terminals:

<http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d>http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d


Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa
Sent: Monday, September 21, 2009 4:56 PM
To: RE-wrenches
Subject: [RE-wrenches] wire gauge reducers

Hi all.....anyone have any recommendations for good lugs useful as <http://www.google.com/search?hl=en&ei=ARG4SvuoOJKAswPmwogb&sa=X&oi=spell&resnum=0&ct=result&cd=1&q=wire+gauge+reducers&spell=1>wire gauge<http://www.google.com/search?hl=en&ei=ARG4SvuoOJKAswPmwogb&sa=X&oi=spell&resnum=0&ct=result&cd=1&q=wire+gauge+reducers&spell=1> reducers? we need to go from #4AWG to #6AWG in the terminals.......specifically we are trying to land our wires in the SMA DC Disconnect which handles a maximum of #6AWG wire size.....
I was hoping for some ideas other than butt connectors......
Thanks!!!
--
Sunny Regards,
Kirpal Khalsa
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to