Chris

Send me a copy too or the link if you have one

Thanks

Bill Hoffer
---- Chris Anderson <cander...@borregosolar.com> wrote: 
> I also have a link to a great FLUKE document on the insulation testing. 
> (meggering wires)
> I can send it to you offline if you would like a copy.
> 
> -Chris Anderson
>   Chief Technology Officer
>   Resources Group
>   C: 603-732-2411
>   Borrego Solar Systems
> 
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Anderson
> Sent: Wednesday, September 16, 2009 2:19 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Insulation testing
> 
> I would like to put forward our commissioning test procedures with regard to 
> voltage and insulation testing for comment and to share if others are trying 
> to tighten up their commissioning procedures. I would love to hear Bill's 
> feedback and any input others might have into our process and areas where we 
> might be exposed.
> Thanks in advance for your comments.
> 
> Sequence and Procedures for
> Quality Assurance Testing and System Commissioning
> 
> Quality Assurance Testing
> o    Source Circuit Testing - Voltage and continuity to ground of all strings
> ·         Test conditions:
> §  Testing to be done at the combiner boxes
> §  Modules are connected to the home runs
> §  Positives are landed on the fuse block, but fuses are not yet installed in 
> the CB
> §  Negatives are  cut to length and labeled but not landed in the CB
> §  Ground is connected in a continuous path to the racking and modules  and 
> is landed in the CB
> ·         Test
> §  Check for voltage between each positive and all negatives - record 
> voltages for each strings and confirm no voltage between strings of different 
> numbers, simultaneously verify polarity as recording voltages
> §  Check for voltage between each positive and ground - record voltage 
> (should be 0)
> §  Check for voltage between each negative and ground - record voltage 
> (should be 0)
> §  Complete the first half of the combiner box commissioning worksheet - 
> noting weather, time of day etc.
> ·         After the test is complete
> §  Each negative can be landed on the negative block in the CB
> §  Test continuity of fuses and insert into holders - DO NOT CLOSE
> 
> o    Output Circuits - Insulation testing of wires from CB to Inverter and 
> verification of polarity
> ·   Test conditions:
> 
>        *   Testing to be done at the inverter
>        *   All wires are run in conduit, cut to length, labeled, spliced if 
> applicable and conduit covers are on from combiner through to inverter
>        *   Only the ground wires are landed in both the CB and the inverter
>        *   The GFDI fuse is removed from the inverter
>        *   All conductors are taped off at the opposite end of where the 
> Megohmeter will be attached and are safely isolated to prevent touching of 
> anything and in a safe position to be energized
> ·   Test
> 
>        *   Megger test all wires to ground at 1000Vdc
>        *   Megger test all wires that share a conduit at any point in the 
> system to each other at 1000Vdc
>        *   record all values and troubleshoot any wires that have a reading 
> under 100 M Ohms  corrected for Temp and humidity
> ·         If under 100 M Ohms  requires investigation and may require 
> replacement of the wire
> ·   After the test is complete
> 
>        *   Land the positive and negative at the combiner box
>        *   Close one fuse holder at CB1 and close the integrated CB/rooftop 
> DC disconnect protecting the output of the CB
>        *   test for voltage and polarity between the positive and negative 
> output circuits from CB1 at the inverter and verify that they are properly 
> labeled
>        *   Open the CB/rooftop DC disconnect and then open the fuse holder in 
> CB#1
>        *   Verify that the voltage has bled down to zero then land the 
> positive and negative wires for this combiner box at the inverter
>        *   Repeat steps for each CB until all polarity and wire locations are 
> identified and landed
>        *   Once all the positive and negative wires from the CB's are landed, 
> if applicable test continuity of the fuses at the inverter disconnect and 
> insert into holders
> 
> o    AC Wiring Circuits - Insulation testing of wires from AC Tie in point 
> (POCC) to Inverter and verification of phasing
> ·   Test conditions:
> 
>        *   Testing to be done at the inverter
>        *   All wires are run in conduit, cut to length, labeled, spliced if 
> applicable and conduit covers are on from AC Point of Connection through to 
> the inverter
>        *   Only the ground wires are landed in both the Main Service Panel 
> and the inverter
>        *   The GFDI fuse is removed from the inverter
>        *   All conductors are taped off at the opposite end of where the 
> Megohmeter will be attached and are safely isolated to prevent touching of 
> anything and in a safe position to be energized
> ·   Test
> 
>        *   Megger test all wires to ground at 1000Vdc
>        *   Megger test all wires that share a conduit at any point in the 
> system to each other at 1000Vdc
>        *   record all values and troubleshoot any wires that have a reading 
> under 100 M Ohms  corrected for Temp and humidity
> ·         If under 100 M Ohms  requires investigation and may require 
> replacement of the wire
> ·   After the test is complete
> 
>        *   Land the conductors in the inverter being sure to follow the 
> inverter manufacturer's guidelines for torque settings and use a permanent 
> marker to create a straight line across the screw indicating the proper 
> torque setting
>        *   This test will likely be completed before the building shut down 
> to interconnect the system.  Do not land the conductors at the AC tie-in 
> point until the panel has been properly de-energized
>        *   After the Service Panel or tie-in point is de-energized, land the 
> conductors at the AC tie-in point.  Be sure to follow the manufacturer's 
> guidelines for proper torque settings and use a permanent marker to create a 
> straight line across the screw indicating the proper torque setting.
> 
> o  Connection testing
> ·   Test conditions:
> 
>        *   Testing to be done at all locations
>        *   All wires are landed
> ·   Test
> 
>        *   Test all wires for proper torque settings - refer to manufacturer 
> installation manual
>        *   Physically tug on all wires for a visual inspection of loose 
> connections
> NOTE - All conductors #4 and larger should be marked with a straight line on 
> the screw once they have been tightened to the appropriate setting
> ·         After the test is complete
> §  Close all fuse holders at each combiner box
> §  Close all DC disconnects associated with each combiner box
> 
> System Commissioning
> o        You are now ready to Commission the inverter
> o    Follow inverter manufacturer commissioning procedures
> o    Complete the balance of the combiner box commissioning worksheet, the 
> initial start up and inverter commissioning worksheet
> 
> 
> ·         Imp Testing of source circuits
> §  Test conditions:
> ·         Testing to be conducted at combiner boxes
> ·         System is up and running
> §  Test
> ·         At each combiner box, check for operating current of each string by 
> placing a clamp meter around each positive source circuit - record the value 
> on the combiner box commissioning worksheet
> ·         Simultaneously record the irradiance value at the plane of the 
> module for the strings of which you are testing
> ·         Repeat for all strings in the combiner box
> 
> §  Imp Testing of output circuits
> §  Test conditions:
> ·         Testing to be conducted at the inverter
> ·         System is up and running
> §  Test
> ·         Check for operating current of each CB output circuit by placing a 
> clamp meter around each positive wire - record the value on the inverter 
> commissioning worksheet
> ·         Simultaneously record the irradiance value at the plane of the 
> representative modules for the combiner box of which you are testing
> ·         Repeat for all output circuits from each combiner box
> 
> 
> 
> -Chris Anderson
>   Chief Technology Officer
>   Resources Group
>   C: 603-732-2411
>   Borrego Solar Systems
> 
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Palumbo
> Sent: Monday, September 14, 2009 10:58 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Insulation testing
> 
> I'd like to see if we can complete the thread on insulation testers 
> (Meggers). Below is a copy of Bill Brooks last posting on this subject from 
> several weeks ago.
> 
> Bill says the keys are to use the tester and in "performing the tests 
> properly and safely which requires test procedures". What are the proper 
> testing procedures? We have a Fluke 1503 and the information that came with 
> it is not very helpful in setting up a testing procedure. The DVD that came 
> with it is more of a sales tool on why you should have the tool. We already 
> have the tool. We want to know how to use the tool. Can anybody give advice 
> on this?
> 
> 
> << I bought two insulation testers (Megger is a brand name) in April. A used
> Fluke 1520 off Ebay for $275 and a new inexpensive (cheap) insulation tester
> on Amazon (Electronic Specialties 550 Insulation Tester for $162). Both work
> fine. The Fluke has better accuracy that I need for very specialized "field
> wet resistance testing" (FWRT). However, the cheap tester works great for
> finding faults in conductors and severe faults in modules.
> 
> I bought both to determine if a cheap meter would work and the answer is
> YES. The key is performing the tests properly and safely which requires test
> procedures. The other key to actually use the tester. Several people own
> these devices, but never use them. They should be used on every installation
> after the wire is installed to determine if any wire damage is visible to
> the tester. Even though this will not solve all field mistakes, it will
> catch the marginal problems that may be too small to be detected by the GFP
> circuit in the inverter.
> 
> Bill. >>
> 
> 
> David Palumbo
> President, Independent Power LLC
> 462 Solar Way Drive, Hyde Park, VT 05655
> NABCEP Certified
> www.independentpowerllc.com
> (802) 888-7194
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to