I see that this install is using EMT, are you using a bonding bushings on the EMT? If so, I had interference on a large PV powered refrigeration unit that used an electronic expansion valve. The wires were installed inside EMT causing all kinds of weird problems. When I removed bonding at both ends & I bonded only one end, similar to when one connects the "drain" conductor on "shielded w/ drain" cat 5 cable, This took care of the problem! Who knows .....tump
-----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel Sent: Wednesday, July 15, 2009 8:12 PM To: RE-wrenches Subject: Re: [RE-wrenches] Inverter AM Interference > solar...@aol.com wrote: > > This is a brand new 5000 US. EMT on all dc runs. The radio is a > BOSE...and is 27 feet away. The interference is runs 24/7... so it > must be AC related. > Does the radio noise go away when you completely disconnect the SMA inverter ? boB _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org