Peter, (back to the Wrenches list)

Yep, 690.47(C) would apply to conventional grid-tied no-battery systems. Sorry for the litany of code references:

690.47(C)(7) does refer to 250.166. As I understand it, you need to size your GEC from your Xantrex ground bar (690.47(C)(5)) per 250.66 and 250.166 (pick whichever requires the larger conductor), as required in 690.47(C)(7). Note that when you're running your AC EGC in the Xantrex units, the installation guide (last I checked) required you to actually run that EGC from the ground bar rather than what looks to be the AC EGC terminal.

DKC


-------- Original Message --------
Subject: Re: [RE-wrenches] What is a "direct-current system"?
From: Peter Parrish <peter.parr...@calsolareng.com>
To: 'Dave Click' <davecl...@fsec.ucf.edu>
Date: 2009/6/19 14:12

No, the inspector is saying that 690.47(B) applies, and as a consequence,
250.166 applies. He didn't mention 690.47(C).

Dave,

I see your point: all conventional grid-tied V systems fall under (C). But
(C) refers to its own set of requirements 690.47(C) (1) through (8) and not
250.166. So which to we follow/

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

-----Original Message----- From: Dave Click [mailto:davecl...@fsec.ucf.edu] Sent: Friday, June 19, 2009 10:50 AM
To: peter.parr...@calsolareng.com
Subject: Re: [RE-wrenches] What is a "direct-current system"?

Peter- Do you mean that since there is a DC circuit as well as an AC circuit, 690.47(*C*) applies? Then 690.47(C)(7) would require your GEC to meet the requirements of 250.66 & 250.166.

I didn't CC the wrenches here, just checking to clarify what you're looking for. I assume that 690.47(A) and (B) being separately listed like that means that 690.47(A) would apply to anything but DC-direct systems, 690.47(B) would apply to everything but AC module systems, and then 690.47(C) is there to clarify that you need to worry about both (A) and (B) for most systems.

DKC

-------- Original Message --------
Subject: [RE-wrenches] What is a "direct-current system"?
From: Peter Parrish <peter.parr...@calsolareng.com>
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Date: 2009/6/19 12:55

I have a LA Dept. of B&S inspector cite Article 690.47(B) "Direct-Current Systems" and its consequent grounding requirements (250.166(A)(B)) in connection with a very straightforward grid tied PV system (i.e. no batteries, just PV and a Xantrex GT inverter).

He said that since there is a DC circuit as well as an AC circuit, 690.47(B) applies. I countered that all PV systems have a DC circuit, so to separately call out a "Direct-Current System" must apply to something other than the DC PV circuit inherent in all PV systems.

Am I missing something here? Is "Direct-Current System" defined in Article 690? We are working off NEC 2008.

Thanks in advance for your help.

-          Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com <mailto:peter.parr...@calsolareng.com> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885


------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to