Hi Jeff,

The Sunny Island 4248U has been discontinued by SMA, and replaced with the 
SI5048U

If you use a transfer switch between the grid and a generator on the SI input, 
make sure that you put in a relay that will prevent the Sunny Boy from 
“selling” power to the generator

Brian Teitelbaum
AEE Solar



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Monday, May 18, 2009 6:15 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island 5048 & Enphase

I am sizing an on-grid with battery backup system that requires using a 
ground-mounted array that will be some distance from the house.  I was favoring 
a Sunny Island with a 4 kW SunnyBoy with AC coupled to allow using a higher 
voltage from the array and the 4 kW Sunny Island  shown in their product 
catalog which is perfect for this project, but all I can find is the Sunny 
Island 5048.

Is the smaller inverter not yet available?    I will also have a backup 
generator with transfer switch feeding this system, so are there any issues 
with the Sunny Island operating from both a generator and the grid depending on 
which is available?

Thanks,

Jeff Yago