Hello Matt,

Both hands up here too. One in the factory and one in the field. I require 
technicians to use the UL 1703 standard dc test potential of 2 times maximum 
system voltage plus 1,000 volts (or 3,000 vdc). Be safe. Wear your gloves.

Joel Davidson
  ----- Original Message ----- 
  From: Matt Lafferty 
  To: 'RE-wrenches' 
  Sent: Monday, April 27, 2009 8:08 PM
  Subject: Re: [RE-wrenches] To Megger or not to Megger


  Hi Keith,

  Both hands up here. From day 1 in PV.

  Every single field-installed current carrying conductor to the point of 
termination. AC & DC. BEFORE energizing them! One megger lead on the conductor, 
the other on the raceway or ground-wire. Megger @ 1kV. Must be greater than 250 
Megohms to pass. Record the values on your commissioning sheet.

  I only meggered the actual arrays on projects where it was a requirement and 
I only did that following specific procedures provided by the module 
manufacturer. No procedure from the mfr = No array megger.

  I believe it's a critical thing to do as part of the commissioning. But then 
again, I don't like ground faults or fires.

  I'll never forget a couple of head scratchers that the megger found.... One 
was a perfectly fine, 6' long piece of Orange #12 XHHW-2 that would only pull 
40 Megohms installed in EMT. Pulled it out and replaced it. Inspected it for 
any visible flaws. None found. Not a scratch or scuff. Used it as a training 
tool for my guys. Hung it on the wall over my desk as a handy reminder. If 
anybody wants a picture...

  The other was interesting, too. The very first PV system I ever installed. 
Was shooting the DC circuits from the inverter all the way to the connector on 
the output jumper cables at the modules. Megger showed dead short on one wire. 
Fluke 79 on ohms showed clear. Hit it with the megger again. Dead short. I'm 
known for being anal about conduit and wire installation, so this was quite 
unexpected, not to mention a little embarrassing. This happened to be a Solarex 
Millennia Integra system with an Omnion inverter and the array happened to be 
scattered all over this roof. For those of you who who have dealt with that 
situation, you'll understand what a cluster-*$#! that is... Especially being my 
very first PV system and all... I wasn't anywhere near confident that I had a 
clue by that point. All ready to see my first install fire up and this happens.

  It was my first install and I had 3 people getting paid prevailing wages to 
learn... I was learning too, but I wasn't making anywhere near prevailing 
wages, let me tell ya. Well, it was early January, late in the day and foggy as 
foggy gets, but we went back onto the roof anyway. Yeah... Overtime for 
everybody but me. We opened up the condulets and J-boxes for inspection. Pulled 
all the wires up out of the J-boxes. Pulled the endcaps and ground clips off 
(unique components of the Integra product). Couldn't find anything suspicious. 
Shot it with the megger again, and it was all clear. But no sign of anything 
that could have been shorted. We put everything back together and shot it 
again. Dead short! Aiyeeeee!

  Call it a day. Go home. I couldn't get back to that site until about the same 
time the next day. Foggy again. Only took 1 helper with me this time. We 
completely repeated the entire exercise, with exactly the same results. By now, 
I was pretty sure this solar stuff wasn't my calling. I've always been regarded 
as a gifted trouble-shooter and all I could say at this point was that I didn't 
know _____! All signs pointed to it being associated with one of the J-boxes or 
the endcaps or the ground clips, but there was NOT a thing we could see. Oh, 
well. I would have to come back another day. When I went back, I took the same 
helper and made sure I had all day if necessary to fix the problem. No matter 
what it turned out to be. We planned to take it apart 1 piece at a time and 
re-shoot it with the megger after each step. I left my helper on the ground 
with the megger while I took it apart on the roof, 1 screw at a time. Again.

  Well, lo and behold, he hollers up that "It's clear" when I pulled the cover 
off one of the 2-gang bell boxes. Hadn't moved a wire. Just took the cover off. 
Let me tell ya, I stuck my nose and four eyes in that box real close, but 
didn't touch any wires. The box was a tight fit with those big, sealant-filled 
blue wire nuts that came with the Solarex Kit, but I still couldn't see 
anything wierd.

  "Shoot it again."

  "All clear, boss."

  I put the cover back on and installed all the screws. "Shoot it again."

  "Dead short." We had a talk later about shouting things like "Dead short" on 
the jobsite, but I won't get into all that right now.

  I took out one of the cover screws. "Shoot it again." Same answer from the 
ground.

  I took out a second screw. "Shoot it again." This time the reply was 
different. I took out the third screw and we repeated the process. Still clear. 
And the fourth. Still clear. WTF? I lifted the cover for what seemed like the 
hundredth time. I studied the nested wires, all neatly and systematically put 
into what I had thought would be their final resting place... Days before and 
time and time again at this point. 

  I began gently lifting the wires out so they all stood up like dandelions in 
a spring lawn. I inspected them for the nth time. Looking for a stray strand 
outside its protective hat. Nope. Overtightened wire nut with the spring or a 
conductor coming out the tip? Nope. But what's this little, nearly 
imperceptible dent in the side of this wire nut? As I looked closer, I could 
see that it was round, flat bottomed and about the same diameter as a 6-32 
screw. Hmmmm. I rolled the wires back into their resting position. Uh, huh. 
This particular wire nut's natural home was directly under the cover screw 
which had cleared the fault when removed and the dent lined up perfectly. The 
screw could just barely be long enough to pierce the plastic and contact the 
wire-spring. 

  I replaced the wire nut, repositioned the conductors to make sure we wouldn't 
have a repeat, and buttoned up the J-box. I put the wirenut in my pocket for 
later reference. One more megger shot proved the system to be all clear. We 
could now energize the DC and do our Voc & Isc testing prior to startup. Thank 
goodness the sun was shining. I wasn't happy about this whole ordeal, but it 
was a good thing we caught it with the megger before we put the power to it.

  That wire nut became the first exhibit in what became my collection of 
training materials for the "what can go wrong and why we do these procedures" 
trainings. Verification that cover and mounting screws cannot come in contact 
with energized equipment was officially put in the checklist. All cover & 
mounting screws in all types of enclosures. There would be no exceptions. There 
would be no excuses. I actually had to write one guy up for a violation of this 
at one point. Good thing we caught that one with the megger before putting the 
power to it.

  I would posit that at least one of the recent PV fires would absolutely have 
been prevented if the installer followed the procedure described above. Too bad 
most don't. Kudos to those of you who do. It's only a matter of time until more 
and more of these AVOIDABLE problems surface.

  If you don't have a megger, get one. If you have one, use it! The Fluke 1520 
is a nice unit. I recommend it over analog models. I cut my teeth with analog 
gear, but really like my 1520. A lot! Rugged instrument that gives you an 
actual number to write on your commissioning sheet. In addition to Megohms, it 
also does VAC, Lo Ohms, Continuity, has a display backlight, Lock and Zero 
functions and my favorite.... Battery Check!  Reads out an actual % value for 
your battery condition. Nice! Uses 4 "C" cells.

  I hope more hands go up on this topic. Thanks for asking, Keith.

  Peace and Palm Trees everybody,

  Matt Lafferty


------------------------------------------------------------------------------
  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin
  Sent: Monday, April 27, 2009 2:37 PM
  To: RE-Wrenches
  Subject: [RE-wrenches] To Megger or not to Megger


  Hi

  I was wondering, by a show of hands, how many of you megger every project?

  Do you have a cut off- like if it is "x" sized system, you will or decide to 
opt out of performing this task?





------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to