Hi Drake, Dont know why not. Meet code as much as possible:
1) AWG of the lightning down conductor adequate? 2) Use non reversible, listed connector to splice array SGEC to down conductor 3) Do you need an additional ground rod? Resistance to earth OK? 4) These rod/rods need to be bonded to the structure grounding electrode system 5) Is there an AHJ? If so, ask for input. Hope this helps. Dick Dick Ratico Solarwind Electric --- You wrote: Can the supplemental grounding electrode conductor be connected to a lightning protection system? We have a case where it would be difficult to run a GEC down a multi story building, but have a convenient copper wire, from a lightning protection system, that runs to a rod. Thank you, Drake Chamberlin Athens Electric OH License 44810 CO License 3773 740-448-7328 740-856-9648 --- end of quote --- Hi _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org