Drake,

Most electricians like to keep the electrical ground and the lightning ground separate which is probably a good idea, but lightning current is likely to follow all paths because earth is common. The best practice is to follow the Code and if the site is in a lightning area, subcontract that part of the work to a local licensed expert (added cost) or put a clause in your contract that protects you from acts of god and specify lightning.

Joel Davidson

----- Original Message ----- From: "Drake Chamberlin" <drake.chamber...@redwoodalliance.org>
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Sent: Friday, March 06, 2009 6:47 AM
Subject: Re: [RE-wrenches] Lightning protection system


I didn't get a reply to the question about connecting the GEC to the lightning protection system on the 8 story building. Although this may seem like an intrinsically dangerous idea, a lightning protection system is required to be bonded to the building grounding electrode system.

"250.106 Lightning Protection Systems.
The lightning protection system ground terminals shall be bonded to the building or structure grounding electrode system."

It would therefore seem that the suplemental ground could connect to that system as well, and in fact use the existing conductor. Any input would be welcome.

Thanks,

Drake




At 09:19 PM 3/4/2009, you wrote:
Hello Wrenches,

Can the supplemental grounding electrode conductor be connected to a lightning protection system?

We have a case where it would be difficult to run a GEC down a multi story building, but have a convenient copper wire, from a lightning protection system, that runs to a rod.

Thank you,

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to