I recently inspected a large ground mount off-grid system about 3 years old 
that was installed by others. I would have used a #6 bare copper ground wire 
due to being exposed almost 100 feet of array length and connected to several 
ground rods with no conduit, but the installer had used #10 which still barely 
met code, but sure was flimsy. Anyway, this small ground wire was sagging down 
in many places along the array length due to about a quarter of the galvanized 
steel self-tapping screws holding the copper against the aluminum had totally 
dissolved. 

We always use the cadmium plated copper grounding blocks and stainless steel 
screws to attach the #6 copper ground wire, and I can see now just how fast the 
galvanic action can dissolve metal when you don't use stainless steel hardware.

Jeff Yago