Hi Dick,
The methods of array grounding that I've used are WEEB bonding
device, or weather resistant grounding lugs screwed to the array
frame or bolted to array frames, using a star washer to dig into the
anodized aluminum frame. The lugs are connected together by a copper
ground wire, which may be smaller than number 6 if mechanical damage
is not an issue.
690.43 only states:
"Devices listed and identified for grounding the metallic frames of
PV modules shall be permitted to bond the exposed metallic frames of
PV modules to grounded mounting structures. Devices identified and
listed for bonding the metallic frames of PV modules shall be
permitted to bond the exposed metallic frames of PV modules to the
metallic frames of adjacent PV modules.
What I've learned, on this list over the years, is that anodized
aluminum can develop a resistive coating, so that some method of
digging into the aluminum, or having a screw threaded into it, must
be utilized to insure good bonding."
An engineer, on a job recently, did not require all the aluminum rail
pieces to be bonded together, since they were bolted together. This
seems consistent with 609.43. Additionally, to do so on that
particular huge racking system would have created a lot of
holes. But here you have an anodized aluminum rail bolted together
without this extra bonding.
My understanding is that we are permitted to use lugs, bolted to the
module frames, utilizing a star washer, rather than having a screw
thread into a hole. This method is certainly permitted in electrical
bonding in general, with or without the star washer. I don't know of
any requirement, for any other anodized aluminum electrical
equipment, to be bonded in this special manner.
Question # 1: Where in the code does it say we need to bond PV
systems in this particular manner? 250.136 (A) permits metal
equipment bolted together to be considered bonded. Are the array
frame bonding methods a UL requirement? If so, is there a place we
can read the actual wording?
Question # 2: If a star washer is sufficient to bond a lug to a
module, why is it not sufficient to bond two modules to each
other? Or, is a star washer not permitted, even though inspectors
accept them. Where can we read what is acceptable?
I'd like to see the wording of the requirement for the extra bonding
of PV modules. Maybe I'm missing something obvious, but I don't find
the requirement spelled out, although do routinely meet it, at least
as I understand it.
Thanks,
Drake
At 09:25 AM 1/7/2009, you wrote:
Hi Drake,
Could you please elaborate?
Dick
Dick Ratico
Solarwind Electric
Bradford, VT
--- You wrote:
Hi William,
So is there no document we can read that delineates the actual
requirements? The standard methods of module bonding that we use
don't always seem logical. Engineers on a recent job had similar feelings.
Drake
At 03:07 PM 1/6/2009, you wrote:
>Drake:
>
>Listed equipment must be installed per the manufacturer's
>instructions. Listing agencies require grounding by a specific
>process to replicate circumstances that occur when the product is tested..
>
>William Miller
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org