Mick,

referring to
there's not an auto-idle switch on that genset which may have accidentally been set for auto, is there?

His generator was actually running in idle mode, operating the household loads when I got there and the first thing I discovered was that the voltage was ~90 volts coming in to the inverter. I manually switched the generator to full speed and then checked the voltage again, that is where I found the rapid fluctuations occurring at the inverter.

Ron

On 27-Dec-08, at 1:23 PM, mick abraham wrote:

Ron wrote: "The owner told me...that someone had wired a switch incorrectly and when he turned it on the system "shut down". He then re-wired it and
everything appeared ok but I'm wondering if this fried a board."

Mick replies: I've seen several times with Outback and other brands (going as far back as the Trace SW) where the inverter responds to an accidental short circuit in the household wiring by shutting itself off quicker than a circuit breaker can open. I'll bet that is what your customer experienced...possibly due to a nicked hot wire in that new switch box shorting out to ground.

I suspect that (part of your customer's report) is completely unrelated to your present problem scenario. If it was my headache I would beg, borrow, or...rent a second generator to insert temporarily instead of the Honda 3800. That's the most conclusive way to determine fault or no-fault on the generator.

Sometimes a genset will operate non-inverter loads OK and will exhibit normal looking voltage etc. but there still could be transients or spikes which
render this input AC power unacceptable to the inverter/charger.

Thinking...there's not an auto-idle switch on that genset which may have
accidentally been set for auto, is there?

Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to