I will look at these for other jobs, our client wants maintenance free on this 
one though.

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
 <http://www.solarwindworks.com/> www.solarwindworks.com
 <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
"Proven Energy Solutions"

 

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 26, 2008 1:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

 

What about the new Surrette FC420's? The latest SOLARPRO mag has a tiny blurb 
on them at the bottom of page 28. Two sets in parallel (630 a/h) would meat 
your criteria and would perform much better than sealed batteries. 

I have been beta testing a set here at home and they seem to be doing fine. I 
hope I get 20 years out of em.

Todd


On Wednesday, November 26, 2008 8:57am, "Chris Worcester" <[EMAIL PROTECTED]> 
said:

With two SI5048’s sucking on this battery bank there is the possibility of some 
serious current transfer taking place. We are proposing an absolute minimum 
battery size that can go full load draw down for three hours, to 50% DOD, my 
inclination is to make this 6 hours. At 3 hours we would need a 500 amp hour 
battery. What are others doing about battery sizing in this scenario? (our 
client hasn’t revealed what loads he wants to back up unfortunately so we are 
approaching this in this manner)

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to