It would seem to me that a properly designed off-grid system with a properly
engineered battery (or other) back-up subsystem would provide a continuous
source of power. One may need to do a load calc to show that the PV system
(under a suitable worst case scenario) can indeed provide the 24 hour load
requirements. 

 

- Peter

Peter T. Parrish, 

California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _____  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Richard
Bogan
Sent: Friday, November 14, 2008 3:20 PM
To: [EMAIL PROTECTED]; RE-wrenches
Subject: Re: [RE-wrenches] permit denined since no grid connection

 

Jeff,

 

I had a couple off-grid installations (newly constructed homes) where the
owners could not get their certificate of occupancy until the off-grid
system was installed and inspected. Once it passed they officially could
move in.

 

Richard

 

  _____  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Yago
Sent: Friday, November 14, 2008 1:14 PM
To: [EMAIL PROTECTED]; RE-wrenches
Subject: Re: [RE-wrenches] permit denined since no grid connection

 


Thank goodness this was not my project, but I just received a call from a
couple that had purchased an old farm house in a rural part of the state
that was almost a mile from utility lines and never had power.  They are
renovating the old farmhouse and applied for all permits from county and
have no problem with having inspections.  However, the electrical permit was
denied on the basis there was "no contineous source of power and this would
not be classified as a weekend type cabin".   Yes, I guess its possible a
local county can make up their own rules, but I am not aware of any
requirement in the NEC, and if there is a specific rule, I would think all
they would need to do is provide information on their proposed
generator/solar/battery/inverter system.

 

We have never had any problems like this in any other counties we have
systems, but before I advise them on how to proceed I wanted to make sure
that there were no specific code requirements other than the electrical
inspection.

 

Have you run into this before?

 

Thanks,

 

Jeff Yagoi

    


 

  _____  

Netscape.  Just the Net You Need.

 
 
The information contained in this message may be confidential and is for the
intended addressee only.
Any unauthorized use, dissemination of the information, or copying of this
message is prohibited. 
If you are not the intended addressee, please notify the sender immediately
and delete this message.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to