My rusty memory was telling me the 4248 was listed by ETL. From my hotel room in sunny San Diego :-), a quick drill-down into ETL's Listed Mark Directory found this: Inverter Charge Controller, Model No. SI4248U. Evaluated to the following...A representative sample of the listed devices have been tested, investigated and found to comply with the requirements of the Standard(s) for Safety Inverters, Converters, & Controllers for Use in Independent Power Systems (UL-1741) and are identified with the ETL Listed Mark. http://etlwhidirectory.etlsemko.com/WebClients/ITS/DLP/products.nsf/6a42 1efeead6f216852568d4005862af/8714764900c91ce78525737f0049ce6e?OpenDocume nt&ExpandSection=2&Highlight=0,SMA#_Section2
Similar for Canada, but with the cETL: http://etlwhidirectory.etlsemko.com/WebClients/ITS/DLP/products.nsf/6a42 1efeead6f216852568d4005862af/81e240dda7c6a59e8525737f0049bbff?OpenDocume nt&ExpandSection=2&Highlight=0,SMA#_Section2 However, I would discuss (nicely) with the AHJ about the reasonableness of their requirement to provide the manufacturer's original certification -- after all, the inverter is either listed to UL1741 or it isn't, and confirming this is a simple matter of looking for the listing mark on the equipment installed. An installer would have to be pretty brave to try to sneak a non-listed inverter through. Pretty soon we'll have to do secret utility-interactive handshakes to prove our worthiness. Although now that I think of it, that certainly would make the floor show this week far more entertaining..... More ocean! More sun! Phil Undercuffler Director, Battery-based and Off-grid Distribution Sales Group Conergy Our World Is Full of Energy 1730 Camino Carlos Rey Suite 103 Santa Fe, NM 87507 [EMAIL PROTECTED] Direct | 505.216.3841 Toll Free | 888.396.6611 x4841 Fax | 505.473.3830 www.conergy.us -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Glenn Burt Sent: Monday, October 13, 2008 11:13 AM To: 'Michael Kelly'; 'RE-wrenches' Subject: Re: [RE-wrenches] SMA Sunny Island Mike, Thanks for the reply, Our utility (National Grid) however has recently started requiring a copy of the original certification issued to the manufacturer of the equipment, so this has been insufficient. As has the cut sheet which bears the ETL stamp, or the web page that said it was tested successfully. We have to submit the UL or other certification for each install we do in their territory at this time. So I need a copy of the certificate issued to SMA for this product - their other certifications are listed on their website, but not this one. -Glenn -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Michael Kelly Sent: Monday, October 13, 2008 12:15 PM To: [EMAIL PROTECTED]; RE-wrenches Subject: Re: [RE-wrenches] SMA Sunny Island Glenn, It meets UL 1741 based on the first paragraph on page 10 of the user manual: http://www.sma-america.com/en_US/products/off-grid-inverters/sunny-islan d-42 48u/dl/U0k0MjQ4VV9NYW51YWw%3D/download.html Best, Mike On Mon, Oct 13, 2008 at 11:26 AM, Glenn Burt <[EMAIL PROTECTED]> wrote: > > Hello esteemed colleagues, > > Can anyone tell me for certain (as in they have seen a copy of it) if the > Sunny Island 4248 has been listed by UL or another NRTL? I can't seem to > find mention of it on the SMA website (although the SI-5048 is there), or > the UL list. > > Thanks for the help! > > > Regards, > > Glenn Burt > Technical Specialist > > Renewable Power Systems, LLC > PO Box 967 > Averill Park, NY 12018 > V: 518-674-5808 > C: 518-810-3174 > F: 518-514-1175 > E: [EMAIL PROTECTED] > www.RPSpower.com > > > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > -- Michael Kelly Project Engineer Project Manager SolarFlair Energy, Inc. 1 Knoll Rd. Hopkinton, MA 01748 Direct Mobile: 617-899-9840 Direct Fax: 781-272-0748 Main Phone: 508-293-4293 Main Fax: 508-293-4003 [EMAIL PROTECTED] _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org