I have installed many Fronius grid-tie systems having a single inverter, but 
recently installed a dual 3K inverter system and are having all kinds of 
problems with the inverters not connecting to grid due to out-of-range grid 
voltage or cycle errors. If we shut down either inverter, the remaining 
inverter usually works fine. The only thing we can identify is the electrician 
may have under-sized the new feeder wiring as we had to run over 150 feet to 
the first breaker panel in a barn, which was another 150 or more feet to the 
main panel and meter base. The sub-panel also serves a large well pump that 
supplies several different buildings and this may be causing some voltage sags. 

We are looking into up-sizing the feeders, but I am still wondering if there 
are other issues or concerns when you have multiple inverters side-by-side at 
the end of a long grid connection.

Thanks,

Jeff Yago

_____________________________________________________________
Netscape.  Just the Net You Need.