> It ismy understanding also that most commercial grade gensets have
> built into the ATS logic that when utility power comesback online, that
> the transfer back to utility power is coordinated with the ATS driving
> the generator until both frequency and phases are within a user
> specified range?


Well, that depends.

If you have a open-transition ATS, where there is a 'neutral' (read: not 
connected to any source) position, it doesn't matter (much). Well, it matters a 
little. There is really two types of open transition.

Something called "open transition" will provide a transfer by going 
closed-open-closed (in both directions). The issue is the open portion of that 
transfer can be very short; sometimes only a few cycles at 60 hz. If you have 
an electric motor connected as load (fan, compressor, whatever), if the sources 
are out of phase, it can be an interesting event for said motor. Typically, a 
open transition switch will wait until the phasing is 'close enough' (usually 
programmable by way of degrees.). We have an old russ electric ats somewhere 
that is happy at about 15 degrees +/-.

There is also a type, "delayed transition", which is closed-open-wait-closed. 
Wait is typically programmable, it may be 500 msec, it might be a minute. It's 
up to the user. This is regarded as the safest type of switch (imho) because 
you do not run the risk of any of the above mentioned badness. However, in a 
datacenter scenario, you do have a battery hit (ranging from tens or hundreds 
of millisecond to many seconds depending on what you want). How good is your 
UPS and battery plant? Will your fans inertia keep air moving for a little 
while? All things to consider.

If you have a closed-transition switch, typically the retransfer from emergency 
to normal is closed-closed, meaning that emergency gen, normal utility, and 
load are all connected together for a short while. Typically in the tens or 
hundreds of msecs. Anything longer than that kinda falls into the cogeneration 
category. That is another discussion.

At least here in JCPL territory (northern NJ), closed transition is frowned 
upon. Too much risk, they think. They are correct, really, but the risk is 
mostly yours. If you lock to the utility out-of-phase, you will surely lose and 
they will surely win. The fault you create that they will see will probably not 
hurt them. Unless it is extraordinarily large and you are very close to the 
nearest substation. You must really trust your utility and your transfer gear 
and your generators to do this. Personally, I'm not a huge fan of this, but 
that is just religion.

Personally, I like delayed transition, and that is what we do on anything 
recent. Short, usually, like 3 or 5 seconds. If anyone wants a demonstration, 
let me know. Long enough for motor controls to say "oh, hey, we lost power so 
let's do a nice soft restart of motors" and compressor controls can do delayed 
restarts as well. Works quite well, in practice.

Much is overlooked in this discussion, as to things people should do about ATS 
and UPS programming.. but it is outside of the scope of NANOG unfortunately. 
Perhaps we need a NADCOG or something. 