On Fri, Mar 5, 2010 at 10:10 PM, Tim Durack <tdur...@gmail.com> wrote: > Same way you cool the top of a rack in a cold/hot aisle system. Blow > cold air up the front of the rack. We measure temperature at select > points in the rack. Keep the hottest spot below set point, and > everything is fine. The physics aren't that much different. > > We are cooling 20kw per rack with this setup. 4 hp c-class chassis per > rack. Works great.
Hi Tim, I poked through AFCO's drawings at http://www.afcosystems.com/pdf/AFCO_Drawings.pdf, How much of a size hit is typical? Do you take the depth out to 52" to create enough space in front of the equipment for air to flow and take the 6-inch hit to the side for the cabling sidecar? What's the impact with respect to sharing the facility with non-AFCO cabinets? I would imagine that with a bunch of these things dynamically changing their air flow it would be hard to maintain a static pressure under the floor. Regards, Bill Herrin -- William D. Herrin ................ her...@dirtside.com b...@herrin.us 3005 Crane Dr. ...................... Web: <http://bill.herrin.us/> Falls Church, VA 22042-3004