The building itself got into the action and their goal was to make a top
notch facility focusing on central patch panel fiber cross connects.
They started with half of the 9th floor originally called MMR-2 and
continued with multiple spaces each bigger as it was quite successful.
No raised floors, properly positioned chillers, ample power, basic but
standard and roomy cabinets, one time fee per cross connect (plus
initial cabling and panel setup OTC) and they have been very succesfull
by all appearances.
Staff reflected their initial goals and I have always interacted well
with them.
Original mmr where each xcon was actualy pulled space to space was quite
a sight with multiple cable conduits and trays running from the tops of
the cabs to the ceiling, all full. New space adopted modern approaches
and looked it.
Joe
Sean Donelan wrote:
ine tume
165 Halsey (and most of its tenant) data centers is an older facility.
Data center practices have changed over the decades, and terminlogy
wasn't standardized until recently.
The biggest FUBAR in telco and data centers is the difference between
"redundancy" and "diversity."
Redundant A/B power feeds are often multiple cables from the same
power source.
Diverse A/B power feeds are cables from different backup power sources
(within limits). 1-utility, 2 battery strings or backup generators.
Often routed through in same conduits/cable trays. But both may be out
of service for scheduled maintenance and some kinds of faults.
Add a spare A/B power feed. Generally a N+1 backup power source and
some additional power switching capability.
Fault tolerant A/B power. Everything from utility to rack is diverse
and redudant (cables, conduit/cable trays, switching equipment and
backup sources). Maintenance can be performed on one of the power
feeds without affecting the other feeds. Does not include redundant
utility feed (not redundant substation, utility).
Cost increase 2x, 5x, 10x
I haven't toured 165 Halsey for 10+ years, so I don't know its current
state. It has multiple tenant data centers, so some may be better
than others.
On Mon, 23 Oct 2023, Babak Pasdar wrote:
Hello,
I wanted to get some feedback as to what is considered standard A/B
power setup when data centers sell redundant power. It has always
been my understanding that A/B power means individually unique and
preferably alternate path connections to disparate UPS units.
A few months ago, 165 Halsey took us down for several hours. They
claimed that a UPS failed causing this issue. Our natural reaction
was that we have A/B redundant power so a failed UPS on the A circuit
should not take down the cabinet. Joe the facility manager claimed
that industry standard A/B power means two circuits to the same UPS,
which makes no sense to me.
They committed to move us to A/B power with redundant circuits to
disparate UPS units. However, we had a multi-hour outage again in
that site this weekend. At first glance it seems to be the same problem.
We have checked with all of our other data center providers who have
confirmed A/B power is in fact individually unique connections to
disparate UPS units. 165 Halsey's definition of what constitutes
redundant power seems unique. Why would anyone pay extra for a second
connection to the same UPS? However, I wanted to get feedback to see
if I am taking crazy pills here 🙂
None-the-less, we have lost all confidence in this facility.
Best Regards,
Babak