NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
OUTAGE ISSUE ON AUGUST 29, 2021
Key Findings
September 8, 2021
https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
Key Findings
[...]
3. Based on the electrical equipment log readings and the manufacturer’s
official assessment, it was determined that the most likely cause of RCC
shutdown was the “Emergency Power Off” button being manually activated.
Secondary Findings
1. The “Emergency Power Off” button did not have a protective cover at the
time of the shutdown or the following WSP investigation.
[...]
Mitigation Steps
1. Set up the electrical equipment Control and Communication systems
properly to stay active so that personnel can monitor RCC electrical
system operations.
[...]