On 2012-02-17, keith <ke...@scott-land.net> wrote:
> In Dell PowerEdge R310's and proably other poweredge servers there's a 
> setting in the bios for power saving that I've set to OS Control.
>
> On Monday a pdu that powers a number of our R310's and some other kit 
> burnt out at the big plug that plugs into the pdu. The Pdu was replaced 
> by the data center staff and when I wen to the data center to plug our 
> servers back in again an "operator" was saying that it's the fan's in 
> the servers that consume all the power.

Power consumption of your equipment shouldn't cause this, there should
be a circuit breaker that trips at a current draw below the maximum
load of PDUs etc in order to protect them.

I would be looking for a proper report from the datacentre/electricians
into why this happened. Simply replacing failed power equipment
without an investigation into what went wrong is not acceptable in
this type of environment.

I would be tempted to set everything to max performance and keep a
close eye on it so that any failures will become clear more quickly,
rather than happen randomly later at an inconvenient moment...