Hello Gokul,

If the control allows access to its registers, you can read the values
and control all timing issues with your LabVIEW application.  Simply
read the registers when you want data or setup a separate loop to read
the values at a specified rate.  However, if directly reading the
registers is not an option, having the PLC dump data over its serial
port is a legitimate way to "link" the two together but there are some
timing issues to consider.  Here is an example using the procedure you
are considering... 

I  recently "linked" a LabVIEW data collection system with PLC data by
simply having the PLC dump data to its serial port at designated times
throughout the test.  The LabVIEW application, which is actually running
on a RT Field Point Module (cFP-2020), monitors the serial port and
brings in the PLC data.  It combines the PLC data with temperature
measurements it is collecting and eventually passes "all" of the data to
another external computer over Ethernet.  We caused the PLC to control
the overall collection rate by dumping data to the serial port each time
a measurement is required.  Hence, the PLC actually triggers or controls
the data sampling rate.

The PLC outputs an ASCII string (the measurement string) which contains
several measurements, a time variable (number of secs since test start),
and terminates with a CRLF.  The output rate is about 10 measurement
strings per second.  I found a baud rate of 17200 worked well.  Note -
if the PLC is going to be outputting data faster than 10 Hz or your
measurement string is long, you will need to increase the baud rate
(transmission rate) or find another alternative.  Additionally, if
timing is critical, you will also need to ensure that you are
"keeping-up" with the instrument.  In my case, the PLC dumps pressure
and flow measurements which are process critical and that need to be
correlated to the temperature measurements.  Therefore, it is necessary
to ensure that all of the measurements (pressure, flow, temp0, temp1,
temp2) are correlated in time (within reason).  However, it is fine, for
this application, to have temperature updates collected at about once
per second (1 Hz) although the pressure and flow are collected at 10 Hz
(during the first five minutes of the test and then at 1 Hz during the
remaining 15 minutes).  By having the PLC control the timing, it enabled
the LabVIEW code to simply monitor the port, grab the completed
measurement sting, combine the other measurement info, and publish the
combined string to an external program and write the sting to disk.

In my opinion, the programming method, using serial communication with
the PLC, should be very similar to what you did with the temperature
controllers although, you may have had to "request" the measurement
string by writing a command to the temp controller and then reading its
response.  I would suggest avoiding this, simply force the PLC to write
and then monitor the port for new info.

Best regards,

Guy R. Hughes
Controlink Systems, LLC

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gokul
Sent: Thursday, May 06, 2004 8:49 AM
To: [EMAIL PROTECTED]
Subject: Keyence and LabView


Hi, 

I am trying to acquire data using LabView from KV16AR
PLCs data memory. A program in PLC is going to dump
data in PLCs data memory and LabView is going to
simultaneously acquire it. The transmission is over
serial port and I have done serial port acquisition
before with temperature controllers. 

I felt both type of acquisition are the same...but
still wanted to ask... Is this any different? ... I
have never worked with PLCs before..thats why wanted
to know.  

TIA
Gokul 


        
                