Hi, Ryan--

On Aug 11, 2010, at 8:51 AM, Ryan Coleman wrote:
> Total: 495W
> 
> According to a calculator if I enter all that information:
> http://www.csgnetwork.com/upssizecalc.html
> It says that it will use 693VA.

That sounds reasonable.  The better PSUs have "80 Plus" certification for 
efficiency, and that's better than the typical wall warts used for modems and 
switches and the like commonly manage.  (The efficiency they're assuming is a 
bit over 70%; using 80% would be around 600VA.)

> Enter that into http://www.csgnetwork.com/batterylifecalc.html
> It requires Amps... 495W  / 120 voltage = 4.125 amps... doesn't seem right 
> but...
> 192 hours... that's not right, right?

Assume for discussion their number was right.  In order to get 495W of output 
load, the UPS needs to provide 693 volt-amps of juice to your equipment.  After 
the inverter and 10:1 stepup transformer used to convert 12VDC or whatever the 
UPS batteries are charged to up to 120VAC, the current needed would be 5.77 
amps.  However, the 12VDC battery source itself would be getting a draw of 57 
amps (ideally; again, the inverter+transformer themselves might only rate about 
90% efficiency for very good quality UPS, so would be drawing more like 60 or 
65 amps).

A standard APC/Tripplite/whatever 700VA UPS tend so have a lead-acid battery 
reasonably similar to a car battery, and typically will have around 100 
amp-hours of charge; they'd probably give you 90 minutes of backup time.  But 
you can look up the detailed specs of specific models and work from their 
amp-hour (or watt-hour) ratings-- actually, I think I'm guestimating more from 
what a 1200VA unit might provide, and a 700VA model is probably going to 
provide more like 40-60 minutes of power...

Regards,
-- 
-Chuck

_______________________________________________
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to "freebsd-questions-unsubscr...@freebsd.org"

Reply via email to